Yes
"from all sources of supply", the transformerless inverter is a source of supply. BOTH legs of all strings should be fused. It has always been that strings shall be protected from all sources of supply, and only SMA had stated that it will not back feed, This nature of the transformerless inverter was commented on before on this list.
I like the approach of breaking all leads so that I can Meger all leads. the PowerOne megers and displays the input lines on start up. I am an electrician, I want to keep getting older and working, I want to have an external to the inverter Disconnect, and fuse all strings.
Thanks as always
DT
--- On Sat, 11/13/10, Eric Thomas <solarepiphany at gmail.com> wrote:
From: Eric Thomas <solarepiphany at gmail.com>
Subject: [RE-wrenches] Head Spinning..(Con) fused.
To: RE-wrenches at lists.re-wrenches.org
Date: Saturday, November 13, 2010, 10:40 PM
Wrenches,
Can anyone shed guidance on the following for me? Should these strings be fused:
Total Modules: 44
Total Strings: 4 strings of 11
Total Inverters: 2
Modules: Silicon Energy 195 Watt @ 8A
Each string feeding an independent MPPT input on an Aurora PVI 4.2kW Inverter (there are 2 / Aurora)
Inverter is transformerless (READ 690.35 (B))
Each strings passes through a shared SolaDeck jbox, no combining, and head directly to their own dedicated GE THN2261RDC DC Disconnect before entering a dedicated MPPT input on the inverter.
My big question is 690.9 (A) exception (b) which states I don't need ocpd as long as "The short circuit currents from all sources do not exceed the ampacity of the conductors."
Because all four strings pass through the same jboxs and conduit before reaching their disconnect and could potentially short together, should I fuse each string?
Or am I just up too late reading code....?
Thanks for being a resource.
--
Eric Thomas
Solar Epiphany LLC
(206) 919-3014
www.solarepiphany.com
-----Inline Attachment Follows-----
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20101114/2f3802a2/attachment-0001.htm>
More information about the RE-Wrenches
mailing list