<table cellspacing="0" cellpadding="0" border="0" ><tr><td valign="top" style="font: inherit;"><DIV>Yes </DIV>
<DIV>"from all sources of supply", the transformerless inverter is a source of supply.&nbsp; BOTH legs of all strings should be fused.&nbsp; It has always been that strings shall be protected from all sources of supply, and only SMA had stated that it will not back feed,&nbsp; This nature of the transformerless inverter&nbsp;was commented on before on this list.&nbsp; <BR></DIV>
<DIV>I like the approach of breaking all leads so that I can Meger all leads.&nbsp; the PowerOne megers and displays the input lines on start up.&nbsp; I am an electrician, I want to keep getting older and working, I want to have an external to the inverter Disconnect, and fuse all strings.&nbsp; </DIV>
<DIV>&nbsp;</DIV>
<DIV>Thanks as always</DIV>
<DIV>DT<BR>--- On <B>Sat, 11/13/10, Eric Thomas <I>&lt;solarepiphany@gmail.com&gt;</I></B> wrote:<BR></DIV>
<BLOCKQUOTE style="BORDER-LEFT: rgb(16,16,255) 2px solid; PADDING-LEFT: 5px; MARGIN-LEFT: 5px"><BR>From: Eric Thomas &lt;solarepiphany@gmail.com&gt;<BR>Subject: [RE-wrenches] Head Spinning..(Con) fused.<BR>To: RE-wrenches@lists.re-wrenches.org<BR>Date: Saturday, November 13, 2010, 10:40 PM<BR><BR>
<DIV id=yiv1658981875>Wrenches,<BR><BR>Can anyone shed guidance on the following for me? Should these strings be fused:<BR><BR>Total Modules: 44<BR>Total Strings: 4 strings of 11 <BR>Total Inverters: 2<BR><BR>Modules: Silicon Energy 195 Watt @ 8A<BR>Each string feeding an independent MPPT input on an Aurora PVI 4.2kW Inverter (there are 2 / Aurora)<BR>Inverter is transformerless (READ 690.35 (B))<BR><BR>Each strings passes through a shared SolaDeck jbox, no combining, and head directly to their own dedicated GE THN2261RDC DC Disconnect before entering a dedicated MPPT input on the inverter.<BR><BR>My big question is 690.9 (A) exception (b) which states I don't need ocpd as long as "The short circuit currents from all sources do not exceed the ampacity of the conductors."<BR><BR>Because all four strings pass through the same jboxs and conduit before reaching their disconnect and could potentially short together, should I fuse each string? <BR><BR>Or am I
 just up too late reading code....?<BR><BR>Thanks for being a resource.<BR clear=all><BR>-- <BR>Eric Thomas<BR>Solar Epiphany LLC<BR>(206) 919-3014<BR><A href="http://www.solarepiphany.com/" rel=nofollow target=_blank>www.solarepiphany.com</A><BR><BR></DIV><BR>-----Inline Attachment Follows-----<BR><BR>
<DIV class=plainMail>_______________________________________________<BR>List sponsored by Home Power magazine<BR><BR>List Address: <A href="http://us.mc519.mail.yahoo.com/mc/compose?to=RE-wrenches@lists.re-wrenches.org" ymailto="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</A><BR><BR>Options &amp; settings:<BR><A href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target=_blank>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</A><BR><BR>List-Archive: <A href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target=_blank>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</A><BR><BR>List rules &amp; etiquette:<BR>www.re-wrenches.org/etiquette.htm<BR><BR>Check out participant bios:<BR>www.members.re-wrenches.org<BR><BR></DIV></BLOCKQUOTE></td></tr></table><br>