[RE-wrenches] battery boxes...and conductor bundling

Phil Undercuffler solarphil at gmail.com
Sun Jul 18 21:08:33 EDT 2010


Off hand, I can think of two components to this -- conductor heating, and
noise/impedance.  From a conductor heating POV, the NEC is fuzzy on specific
distance but the general rule is to not bundle conductors for lengths
greater than 18', or standard derates would need to be applied.  With the
costs of copper, I think you'd want to avoid unnecessary increasing of cable
size wherever possible.

>From a noise and impedance POV, I'd ditto what William Miller says but add
twisting the cables if possible, and with the possible additional caveat of
conductors of opposite polarity *serving the same device*.  In most systems
the DC negative (usually) conductors are common and therefore this might be
moot, but it is theoretically possible to have a system with discrete
components and discrete conductors.  (Not sure what that system would look
like, but just thinking out loud here...)  In any case, in such a system
bundling the positive of one inverter with the negative of another inverter
probably won't have the positive impact desired.

Phil Undercuffler



On Sun, Jul 18, 2010 at 11:40 AM, Tom DeBates <habitek83 at yahoo.com> wrote:

> hello Wrenches,
>   Since we usually are using the batteries in back-up applications and thus
> AGM batteries, we like to stack them. So we make-up a steel (2"X2" angle)
> rack, have our tinner bend-up an enclosure, and get all parts powder coated.
> Expensive, but last forever.
>   On another note; what is the skinny on bundling conductors of same
> polarity?.....Ok, bad?  Searched the archives and the Internets and couldn't
> find a satisfactory answer.
> thanks,
> tom
>
> Tom DeBates
> Habi-Tek
> 524 Summit St.
> Geneva,IL. 60134
> 630-262-8193
> fax 630-262-1343
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20100718/9b4f61cd/attachment-0001.htm>


More information about the RE-Wrenches mailing list