Off hand, I can think of two components to this -- conductor heating, and noise/impedance. From a conductor heating POV, the NEC is fuzzy on specific distance but the general rule is to not bundle conductors for lengths greater than 18&#39;, or standard derates would need to be applied. With the costs of copper, I think you&#39;d want to avoidunnecessaryincreasing of cable size wherever possible.<div>
<br></div><div>From a noise and impedance POV, I&#39;d ditto what William Miller says but add twisting the cables if possible, and with the possible additional caveat of conductors of opposite polarity <i>serving the same device</i>. In most systems the DC negative (usually) conductors are common and therefore this might be moot, but it is theoretically possible to have a system with discrete components and discrete conductors. (Not sure what that system would look like, but just thinking out loud here...) In any case, in such a system bundling the positive of one inverter with the negative of another inverter probably won&#39;t have the positive impact desired.</div>
<div><br></div><div>Phil Undercuffler<br><div><br></div><div><br><br><div class="gmail_quote">On Sun, Jul 18, 2010 at 11:40 AM, Tom DeBates <span dir="ltr">&lt;<a href="mailto:habitek83@yahoo.com">habitek83@yahoo.com</a>&gt;</span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;"><table cellspacing="0" cellpadding="0" border="0"><tbody><tr><td valign="top" style="font:inherit">hello Wrenches,<br>
 Since we usually are using the batteries in back-up applications and thus AGM batteries, we like to stack them. So we make-up a steel (2&quot;X2&quot; angle) rack, have our tinner bend-up an enclosure, and get all parts powder coated. Expensive, but last forever.<br>
 On another note; what is the skinny on bundling conductors of same polarity?.....Ok, bad? Searched the archives and the Internets and couldn&#39;t find a satisfactory answer.<br>thanks,<br>tom <br><br>Tom DeBates<br>
Habi-Tek<br>
524 Summit St.<br>
Geneva,IL. 60134<br>
    630-262-8193<br>
fax 630-262-1343</td></tr></tbody></table><br>

      <br>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br></div></div>