One set of batteries in a series string is best. two paralleled strings are OK, three are marginal, four or more is just a bad idea and it's nearly impossible to get them to play nice together for long.
Good Luck, bob-O
On Jun 22, 2010, at 5:15 PM, Mark Frye wrote:
Thanks Phil,
I really appreciate all the input I am getting.
As I mentioned, these are not the Solar One batteries, they are forklift batteries, so I am not even going to talk to NWES.
I am working with the regional Enersys service center to have a guy out to cut and re-weld the interconnects after the cell is replaced. If they want to help me out because the battery is still within the 5/2 forklift warranty period, that will be fine.
Everything you say makes sense. The owner is on-board with spending more time and effort in order to care for the batteries and I am working up a plan to do that.
At this point it looks something like:
- Replace the bad cell and continue with the 4 string system size
- Give the bank a full EQ charge. I like your set points of 62-64 V for 3 to 4 hours (just don't get the cells too hot). I would really like to see all the cells up to 1.280 for once. I can break the bank down to it's individual strings to do this, in order to give it a bit more punch
- Review and adjust the charge settings 2 to 4 times a year to optimize for seasonal changes in ambient temperatures and load profiles. This might include adjusting the volt start settings to insure that the generator is running more often (every 7-10 days sounds good to me); extending the absorb time as much as possible (staying above 50% load on the generator).
- Giving an EQ charge as above once every 4 to 8 weeks.
I imagine that in this way they will muddle along fine for quite sometime. When a major capital component needs to be replaced they can make the best choice at that time.
I like a lot of the other ideas that have come up such as more ventilation, both of the room and the inverters.
Please any more thoughts you may have.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Phil Undercuffler
Sent: Tuesday, June 22, 2010 4:29 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] For Big Bank Off Grid System Connoisseurs
I'm still not clear on why everyone thinks that this is a failure which should be covered under warranty. If Rob or Jean want to give a free cell, then that's above and beyond -- but I don't think we should be blaming the battery in this case.
Let's explore the situation. We've got 6760 AH of battery storage, in four parallel strings. Four strings in parallel would not be my recommendations, but let's leave that aside for now. The solar, if putting out full rated wattage with no degradation due to heat, off-axis, shading, soiling, or any other loss will put out a whopping 100 amps, for a mind boggling C/67. Add normal derates, and we're down to a C/80 charge rate, and we haven't even accounted for daytime loads. The solar is there for show, and to make the owners feel green.
So how about the generator charging? We have 10 Outback inverters -- that should be enough, right? Well, 10x45A each gives us a C/15 charge rate, which should be OK. But is the generator large enough? That's a lot of inverters to drive, this load is pretty reactive, and we've not any information about the background AC loads except that they're probably pretty large. Wait, the generator is only 30kVA, which is only good for 24kVA of continuous resistive load (30*.08). What's the altitude of the installation -- if it's higher than 1,000 feet the generator should be further derated. No inverter is as efficient at charging as it is at inverting, so of that 24kVA of available generator capacity, only 19kVA is likely to make it to the batteries -- that's a likely C/21 charge rate if there were no AC loads, but there are, so it's likely to be lower.
And when do the batteries get charged? Not every day -- the solar can barely keep up with the self discharge. The generator runs every 2 - 3 weeks, so the batteries are in a state of near constant discharge for 14 - 21 days on average. When they get so low they hit the AGS floor, the generator kicks in. However, just as the battery voltage climbs to the beginning of the absorption state, the generator is shut off.
These batteries haven't been full in over six years. They haven't received a proper charge in over six years, either. I'm surprised they've lasted as long as they have. Let me guess the last time they were equalized -- really equalized, not just "I hit the button and ran the generator until I got tired of the noise" equalized -- as in charge until the voltage rises up to 62-64 volts for 3 or 4 hours, and the specific gravity on each and every cell hits 1.265. Was the bank commissioned with an EQ upon installation?
I think that one of the best things that can be done to serve these clients (other than recommend a huge investment in efficiency) is to decrease the time between generator charges by 50-75%. You want to get it to the point where the generator is cycling on at least every 7-10 days. In addition, you really want to extend the absorption time -- 12 minutes is just not enough to do anything but tease. The customer really needs a bigger generator to drive this system, too. Adding vent fans to the power room is highly recommended -- you're dissipating something like 6,000 watts of heat when you're running 10 inverters at full charge. Power the vent fans off the generator output, so they only come on when the system is charging.
When it's time to replace this bank of batteries, I'd recommend looking at decreasing the size of the bank by 50%. And investing more in efficiency, of course.
Hope this helps,
Phil Undercuffler
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette: