<html><head></head><body style="word-wrap: break-word; -webkit-nbsp-mode: space; -webkit-line-break: after-white-space; ">One set of batteries in a series string is best. two paralleled strings are OK, three are marginal, four or more is just a bad idea and it's nearly impossible to get them to play nice together for long.<div>Good Luck, bob-O</div><div><br><div><div>On Jun 22, 2010, at 5:15 PM, Mark Frye wrote:</div><br class="Apple-interchange-newline">
<div>
<div dir="ltr" align="left"><span class="453163923-22062010"><font color="#0000ff" size="2" face="Arial">Thanks Phil,</font></span></div>
<div dir="ltr" align="left"><span class="453163923-22062010"><font color="#0000ff" size="2" face="Arial"></font></span>&nbsp;</div>
<div dir="ltr" align="left"><span class="453163923-22062010"><font color="#0000ff" size="2" face="Arial">I really appreciate all the input I am 
getting.</font></span></div>
<div dir="ltr" align="left"><span class="453163923-22062010"><font color="#0000ff" size="2" face="Arial"></font></span>&nbsp;</div>
<div dir="ltr" align="left"><span class="453163923-22062010"><font color="#0000ff" size="2" face="Arial">As I mentioned, these are not the Solar One batteries, they 
are forklift batteries, so I am not even going to talk to 
NWES.</font></span></div>
<div dir="ltr" align="left"><span class="453163923-22062010"><font color="#0000ff" size="2" face="Arial"></font></span>&nbsp;</div>
<div dir="ltr" align="left"><span class="453163923-22062010"><font color="#0000ff" size="2" face="Arial">I am working with the regional Enersys service center to have 
a guy out to cut and re-weld the interconnects after the cell is replaced. If 
they want to help me out because the battery is still within the 5/2 forklift 
warranty period, that will be fine.</font></span></div>
<div dir="ltr" align="left"><span class="453163923-22062010"><font color="#0000ff" size="2" face="Arial"></font></span>&nbsp;</div>
<div dir="ltr" align="left"><span class="453163923-22062010"><font color="#0000ff" size="2" face="Arial">Everything you say makes sense.&nbsp; The owner is on-board 
with spending more time and effort in order to care for the batteries and I am 
working up a plan to do that.</font></span></div>
<div dir="ltr" align="left"><span class="453163923-22062010"><font color="#0000ff" size="2" face="Arial"></font></span>&nbsp;</div>
<div dir="ltr" align="left"><span class="453163923-22062010"><font color="#0000ff" size="2" face="Arial">At this point it looks something like:</font></span></div>
<div dir="ltr" align="left"><span class="453163923-22062010"><font color="#0000ff" size="2" face="Arial"></font></span>&nbsp;</div>
<div dir="ltr" align="left"><span class="453163923-22062010"><font color="#0000ff" size="2" face="Arial">- Replace&nbsp;the bad cell and continue with the 4 string 
system size</font></span></div>
<div dir="ltr" align="left"><span class="453163923-22062010"><font color="#0000ff" size="2" face="Arial">- Give the bank a full EQ charge. I like your set points of 
62-64 V for 3 to 4&nbsp;hours (just don't get the cells too hot).&nbsp;I would 
really like to see all the cells up to 1.280 for once. I can break the bank down 
to it's individual strings to do this,&nbsp;in order to give it a&nbsp;bit more 
punch</font></span></div>
<div dir="ltr" align="left"><span class="453163923-22062010"><font color="#0000ff" size="2" face="Arial">- Review and adjust the charge settings 2 to 4 times a year to 
optimize for seasonal changes in ambient temperatures and load profiles. This 
might include adjusting the volt start settings to insure that the generator is 
running&nbsp;more often&nbsp;(every 7-10 days sounds good to me); extending the 
absorb time as much as possible (staying above 50% load on the 
generator).</font></span></div>
<div dir="ltr" align="left"><span class="453163923-22062010"><font color="#0000ff" size="2" face="Arial">- Giving an EQ charge as above once every 4 to 8 
weeks.</font></span></div>
<div dir="ltr" align="left"><span class="453163923-22062010"><font color="#0000ff" size="2" face="Arial"></font></span>&nbsp;</div>
<div dir="ltr" align="left"><span class="453163923-22062010"><font color="#0000ff" size="2" face="Arial">I imagine that in this way they will muddle along fine for 
quite sometime. When a major capital component needs to be replaced 
they&nbsp;can make the best choice at that time.</font></span></div>
<div dir="ltr" align="left"><span class="453163923-22062010"><font color="#0000ff" size="2" face="Arial"></font></span>&nbsp;</div>
<div dir="ltr" align="left"><span class="453163923-22062010"><font color="#0000ff" size="2" face="Arial">I like a lot of the other ideas that have come up such as more 
ventilation, both of the room and the inverters.</font></span></div>
<div dir="ltr" align="left"><span class="453163923-22062010"><font color="#0000ff" size="2" face="Arial"></font></span>&nbsp;</div>
<div dir="ltr" align="left"><span class="453163923-22062010"><font color="#0000ff" size="2" face="Arial">Please any more thoughts you may have.</font></span></div>
<div dir="ltr" align="left"><font color="#0000ff" size="2" face="Arial"></font><br><span lang="en-us"><font size="2" face="Arial">Mark Frye</font></span> <br><span lang="en-us"><font size="2" face="Arial">Berkeley Solar Electric Systems</font></span> 
<br><span lang="en-us"><font size="2" face="Arial">303 Redbud Way</font></span> 
<br><span lang="en-us"><font size="2" face="Arial">Nevada City,&nbsp; CA 
95959</font></span> <br><span lang="en-us"><font size="2" face="Arial">(530) 
401-8024</font></span> <br><span lang="en-us"></span><a href="http://www.berkeleysolar.com/"><span lang="en-us"><u><font color="#0000ff" size="2" face="Arial">www.berkeleysolar.com</font></u></span></a><span lang="en-us"><font size="2" face="Arial">&nbsp;</font></span> </div>
<div>&nbsp;</div><br>
<div dir="ltr" lang="en-us" class="OutlookMessageHeader" align="left">
<hr tabindex="-1">
<font size="2" face="Tahoma"><b>From:</b> <a href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a> 
[mailto:re-wrenches-bounces@lists.re-wrenches.org] <b>On Behalf Of </b>Phil 
Undercuffler<br><b>Sent:</b> Tuesday, June 22, 2010 4:29 PM<br><b>To:</b> 
RE-wrenches<br><b>Subject:</b> Re: [RE-wrenches] For Big Bank Off Grid System 
Connoisseurs<br></font><br></div>
<div></div>I'm still not clear on why everyone thinks that this is a failure 
which should be covered under warranty. &nbsp;If Rob or Jean want to give a free 
cell, then that's above and beyond -- but I don't think we should be blaming the 
battery in this case.&nbsp; 
<div><br>Let's explore the situation. &nbsp;We've got 6760 AH of battery 
storage, in four parallel strings. &nbsp;Four strings in parallel would not be 
my recommendations, but let's leave that aside for now. &nbsp;The solar, if 
putting out full rated wattage with no degradation due to heat, off-axis, 
shading, soiling, or any other loss will put out a whopping 100 amps, for a mind 
boggling C/67. &nbsp;Add normal derates, and we're down to a C/80 charge rate, 
and we haven't even accounted for daytime loads. &nbsp;The solar is there for 
show, and to make the owners feel green.</div>
<div><br></div>
<div>So how about the generator charging? &nbsp;We have 10 Outback inverters -- 
that should be enough, right? &nbsp;Well, 10x45A each gives us a C/15 charge 
rate, which should be OK. &nbsp;But is the generator large enough? &nbsp;That's 
a lot of inverters to drive,&nbsp;this load is pretty reactive,&nbsp;and we've 
not any information about the background AC loads except that they're probably 
pretty large. &nbsp;Wait, the generator is only 30kVA, which is only good for 
24kVA of continuous resistive load (30*.08). &nbsp;What's the altitude of the 
installation -- if it's higher than 1,000 feet the generator should be further 
derated. &nbsp;No inverter is as efficient at charging as it is at inverting, so 
of that 24kVA of available generator capacity, only 19kVA is likely to make it 
to the batteries -- that's a likely C/21 charge rate if there were no AC loads, 
but there are, so it's likely to be lower.</div>
<div><br></div>
<div>And when do the batteries get charged? &nbsp;Not every day -- the solar can 
barely keep up with the self discharge. &nbsp;The generator runs every 2 - 3 
weeks, so the batteries are <b>in a state of near constant discharge for 14 - 21 
days on average</b>. &nbsp;When they get so low they hit the AGS floor, the 
generator kicks in. &nbsp;However, just as the battery voltage climbs to the 
beginning of the absorption state, the generator is shut off. &nbsp;</div>
<div><br></div>
<div>These batteries haven't been full in over six years. &nbsp;They haven't 
received a proper charge in over six years, either. &nbsp;I'm surprised they've 
lasted as long as they have. &nbsp;Let me guess the last time they were 
equalized -- really equalized, not just "I hit the button and ran the generator 
until I got tired of the noise" equalized -- as in charge until the voltage 
rises up to 62-64 volts for 3 or 4 hours, and the specific gravity on each and 
every cell hits 1.265. &nbsp;Was the bank commissioned with an EQ upon 
installation? &nbsp;</div>
<div><br></div>
<div>I think that one of the best things that can be done to serve these clients 
(other than recommend a huge investment in efficiency) is to decrease the time 
between generator charges by 50-75%. You want to get it to the point where the 
generator is cycling on at least every 7-10 days. &nbsp;In addition, you really 
want to extend the absorption time -- 12 minutes is just not enough to do 
anything but tease. &nbsp;The customer really needs a bigger generator to drive 
this system, too. &nbsp;Adding vent fans to the power room is highly recommended 
-- you're&nbsp;dissipating something like 6,000 watts of heat when you're 
running 10 inverters at full charge. &nbsp;Power the vent fans off the generator 
output, so they only come on when the system is charging.</div>
<div>
<div><br></div>
<div>When it's time to replace this bank of batteries, I'd recommend looking at 
decreasing the size of the bank by 50%. &nbsp;And investing more in efficiency, 
of course.&nbsp;</div>
<div><br></div>
<div>Hope this helps,</div>
<div><br></div>
<div>Phil Undercuffler</div></div></div>
_______________________________________________<br>List sponsored by Home Power magazine<br><br>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br><br>Options &amp; settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<br><br>List rules &amp; etiquette:<br>www.re-wrenches.org/etiquette.htm<br><br>Check out participant bios:<br>www.members.re-wrenches.org<br><br></div><br></div></body></html>