[RE-wrenches] Enphase System Labeling
R Ray Walters
ray at solarray.com
Mon May 17 17:07:00 EDT 2010
I only use this signage, when its true.
Gridtie inverters interrupt output in milliseconds, so I don't use it on AC.
My understanding is that it does apply to array disconnects, as the inverter capacitors could still have a charge, that would render the "live on both sides" idea true on DC.
I also see this as appropriate signage in some battery based situations.
Personally, I see a serious problem with too much signage: people won't read any of it, if there's too much.
R. Walters
ray at solarray.com
Solar Engineer
On May 17, 2010, at 2:47 PM, Dave Click wrote:
> Quick poll- how many inspectors/utilities out there require the "live on both sides" label for AC Disconnects, even after you explain to them this only applies to DC disconnects? Even though it's inaccurate, I feel that it at least gives unqualified personnel pause before they open up a switch to something they don't understand.
>
> DKC
>
> Dana wrote:
>> This was our last batch
>>
>> *Labeling For Grid-tie Solar Electric System*
>>
>> *Great Solar Works, Inc., 970-626-5253*
>>
>> * *
>>
>> * KNOPP SIGNS ***
>>
>> * *
>>
>> *Qty – 2, Color red*
>>
>> * *
>>
>> *INTERACTIVE SYSTEM POINT OF INTERCONNECTION*
>>
>> *Enphase Micro-Inverters [1] per module [17] Total*
>>
>> * *
>>
>> *PHOTOVOLTAIC SYSTEM SOURCE*
>>
>> * *
>>
>> * PV System Total Watts 3.910 KW*
>>
>> * Maximum AC Output Operating Current 13.6 Amps*
>>
>> * AC Operating Voltage 240 Volts *
>>
>> * *
>>
>> *For information and service contact: *
>>
>> *Great Solar Works, Inc., 970-626-5253*
>>
>> * *
>>
>> *Qty – 1, Color red*
>>
>> * *
>>
>> *PHOTOVOLTAIC SYSTEM SOURCE*
>>
>> * *
>>
>> * PV System Total Watts 3.910 KW*
>>
>> * Maximum AC Output Operating Current 13.6 Amps*
>>
>> * AC Operating Voltage 240 Volts *
>>
>> * *
>>
>> *For information and service contact: *
>>
>> *Great Solar Works, Inc., 970-626-5253*
>>
>> * *
>>
>> *Qty – 1, Color red*
>>
>> * *
>>
>> *PHOTOVOLTAIC AC SYSTEM UTILITY DISCONNECT*
>>
>> *WARNING - ELECTRIC SHOCK HAZARD - DONOT TOUCH TERMINALS.*
>>
>> *TERMINALS ON BOTH THE LINE AND LOAD SIDES MAY BE ENERGIZED*
>>
>> *IN THE OPEN POSITION. IF A GROUND FAULT IS INDICATED THE NORMALLY
>> GROUNDED CONDUCTORS MAY BE ENERGIZED AND UNGROUNDED*
>>
>> * *
>>
>> *For information and service contact: *
>>
>> *Great Solar Works, Inc., 970-626-5253*
>>
>> * *
>>
>> *Qty -1, Color Yellow*
>>
>> * *
>>
>> *PHOTOVOLTAIC SYSTEM CONNECTED*
>>
>> *THE AC PV DISCONNECT IS LOCATED *
>>
>> *Next to Meter on South Wall *
>>
>> *For information and service contact: *
>>
>> *Great Solar Works, Inc., 970-626-5253*
>>
>> * *
>>
>> Thanks, Dana Orzel
>>
>> Great Solar Works, Inc
>>
>> E - dana at solarwork.com
>>
>> V - 970.626.5253
>>
>> F - 970.626.4140
>>
>> C - 970.209.4076
>>
>> web - www.solarwork.com
>>
>> Responsible Technologies for Responsible People since 1988"
>>
>>
>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Options& settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules& etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
More information about the RE-Wrenches
mailing list