[RE-wrenches] Enphase System Labeling

Dave Click daveclick at fsec.ucf.edu
Mon May 17 16:47:51 EDT 2010


Quick poll- how many inspectors/utilities out there require the "live on 
both sides" label for AC Disconnects, even after you explain to them 
this only applies to DC disconnects? Even though it's inaccurate, I feel 
that it at least gives unqualified personnel pause before they open up a 
switch to something they don't understand.

DKC

Dana wrote:
> This was our last batch
>
> *Labeling For Grid-tie Solar Electric System*
>
> *Great Solar Works, Inc., 970-626-5253*
>
> * *
>
> * KNOPP SIGNS ***
>
> * *
>
> *Qty – 2, Color red*
>
> * *
>
> *INTERACTIVE SYSTEM POINT OF INTERCONNECTION*
>
> *Enphase Micro-Inverters [1] per module [17] Total*
>
> * *
>
> *PHOTOVOLTAIC SYSTEM SOURCE*
>
> * *
>
> * PV System Total Watts 3.910 KW*
>
> * Maximum AC Output Operating Current 13.6 Amps*
>
> * AC Operating Voltage 240 Volts *
>
> * *
>
> *For information and service contact: *
>
> *Great Solar Works, Inc., 970-626-5253*
>
> * *
>
> *Qty – 1, Color red*
>
> * *
>
> *PHOTOVOLTAIC SYSTEM SOURCE*
>
> * *
>
> * PV System Total Watts 3.910 KW*
>
> * Maximum AC Output Operating Current 13.6 Amps*
>
> * AC Operating Voltage 240 Volts *
>
> * *
>
> *For information and service contact: *
>
> *Great Solar Works, Inc., 970-626-5253*
>
> * *
>
> *Qty – 1, Color red*
>
> * *
>
> *PHOTOVOLTAIC AC SYSTEM UTILITY DISCONNECT*
>
> *WARNING - ELECTRIC SHOCK HAZARD - DONOT TOUCH TERMINALS.*
>
> *TERMINALS ON BOTH THE LINE AND LOAD SIDES MAY BE ENERGIZED*
>
> *IN THE OPEN POSITION. IF A GROUND FAULT IS INDICATED THE NORMALLY
> GROUNDED CONDUCTORS MAY BE ENERGIZED AND UNGROUNDED*
>
> * *
>
> *For information and service contact: *
>
> *Great Solar Works, Inc., 970-626-5253*
>
> * *
>
> *Qty -1, Color Yellow*
>
> * *
>
> *PHOTOVOLTAIC SYSTEM CONNECTED*
>
> *THE AC PV DISCONNECT IS LOCATED *
>
> *Next to Meter on South Wall *
>
> *For information and service contact: *
>
> *Great Solar Works, Inc., 970-626-5253*
>
> * *
>
> Thanks, Dana Orzel
>
> Great Solar Works, Inc
>
> E - dana at solarwork.com
>
> V - 970.626.5253
>
> F - 970.626.4140
>
> C - 970.209.4076
>
> web - www.solarwork.com
>
> Responsible Technologies for Responsible People since 1988"
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options&  settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules&  etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>


More information about the RE-Wrenches mailing list