[RE-wrenches] Square D DC disconnects
David Brearley
david.brearley at solarprofessional.com
Mon Jan 11 19:51:10 EST 2010
Right, Kent, but 690.4(D) does require the use of products ³identified and
listed for the application.² So, for example, UL-listed combiner boxes are
required per NEC 2008, whereas integrators could previously site build
combiners using UL-listed parts. The appropriate listing for a PV combiner,
everyone agrees, is UL1741. This code article lists most major components in
a PV system, but not discos. I¹m simply wondering if there is some activity
I am unaware of seeking to add dc discos to this list or to the UL1741
standard. Just curious.
On 1/11/10 6:27 PM, "Kent Osterberg" <kent at coveoregon.com> wrote:
> David,
>
> The NEC doesn't require UL listing. The most appropriate section of the code
> about this is Article 110, Requirements for Electrical Installations, it
> requires equipment to be approved. In many jurisdictions, such as Oregon,
> that means evaluated and approved by a testing lab such as UL.
>
> Kent Osterberg
> Blue Mountain Solar, Inc.
>
>
> David Brearley wrote:
>> Re: [RE-wrenches] Square D DC disconnects Thanks, Bill.
>>
>> Glad to hear you think the HU series is still a good option.
>>
>> When I was making the rounds at SPI, I stopped by the Eaton booth and got the
>> sense that they were gunning for Square D. They made light of Square D¹s
>> self-certification of the HU series discos. The rep also made a statement
>> about the new Eaton dc discos being the only ones designed to meet UL1741
>> requirements. When I got home, the first thing I looked up was 690.4(D). This
>> doesn¹t say anything about dc disconnects needing to be listed to some
>> special PV standard.
>>
>> Is there a movement in this direction? Is there a UL1741 standard for dc
>> discos that is somehow different that the standard used for other dc
>> disconnects?
>>
>> Best,
>>
>> David
>>
>> On 1/11/10 5:28 PM, "Bill Brooks" <billbrooks7 at yahoo.com> wrote:
>>
>>
>>> David and Kirpal,
>>>
>>> It is ultimately up to the AHJ whether or not they accept the
>>> Schneider/Square D self certification. That is a judgment call the installer
>>> needs to clear with the AHJ. That being said, having Square D behind the
>>> rating of a switch is a whole lot more than any one of the smaller companies
>>> making equipment for the PV industry.
>>>
>>> I will continue to use the 30, 60, and 100-amp versions in the way
>>> recommended by the manufacturer because it is a huge saving in cost and they
>>> are well made switches. I will also check with the local AHJ before
>>> installing them in case they are not going to pass it. You have to remember
>>> you are working with one of the largest electrical suppliers in the world.
>>> They have a huge reputation with local jurisdictions.
>>>
>>> Eaton has been in the process of trying to make a big deal out of this issue
>>> since they want a piece of the market. Fortunately, they are starting to
>>> build products specifically for the PV industry, which I applaud. However,
>>> they need to be given a hard time for the way they have tried to imply that
>>> all Square D switches are not properly listed. They won¹t admit to that
>>> because they would end up in a legal battle, but that is essentially what
>>> they have been doing. Square D still has the largest selection of dc-rated
>>> equipment on the market. Eaton has a long way to go.
>>>
>>> In a recent project that I reviewed, the engineer pulled the Square D
>>> 400-amp disconnect and replaced it with an Eaton disconnect at the
>>> insistence of the Eaton rep. The Eaton product was not properly rated or
>>> listed for the voltage while the Square D product was. This is the insanity
>>> that needs to stop.
>>>
>>> Bill.
>>>
>>>
>>>
>>> From: re-wrenches-bounces at lists.re-wrenches.org
>>> [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of David
>>> Brearley
>>> Sent: Monday, January 11, 2010 11:39 AM
>>> To: RE-wrenches
>>> Subject: Re: [RE-wrenches] Square D DC disconnects
>>>
>>> Kirpal,
>>>
>>> Have you checked out the SolarBOS disconnecting combiners? Their 28A version
>>> might be ideal for large resi or small commercial applications. For larger
>>> projects, Blue Oak PV Products and AMtec Solar also have disconnecting
>>> combiners.
>>>
>>> Thanks for sharing the updated Square D tech note. I had no idea that the
>>> Square D HU Series disconnects were not UL-listed when used as described in
>>> the older tech notes. The fact that this is not a UL-listed use of the heavy
>>> duty safety switch, pretty much means that it is not an option for
>>> integrators. As far as I know, there is no other product that is listed for
>>> this use.
>>>
>>> David Brearley, Senior Technical Editor
>>> SolarPro magazine
>>> NABCEP Certified PV Installer
>>> david.brearley at solarprofessional.com
>>>
>>>
>>> On 1/9/10 4:14 PM, "Kirpal Khalsa" <solarworks at gmail.com> wrote:
>>>
>>>> Hi All......
>>>>
>>>
>>> I recently came across a revised technical bulletin from square D (
>>> http://ecatalog.squared.com/pubs/Electrical%20Distribution/Safety%20Switches
>>> /Heavy%20Duty/3110DB0401.pdf )......we have for years been using the Square
>>> D DC Disconnect of various amperages (30, 60, 100) as disconnects leading
>>> upto the inverter from the array.....we have frequently wired one string to
>>> each of the three poles of the disconnect......we have had this
>>> configuration inspected by inspectors regularly with approval
>>> everytime......this new revision of the document from Square D shows this is
>>> no longer a UL listed method.....they are now stating in this document that
>>> they are "self certifying" this technique.......have any of you come across
>>> this or know why Square D has back tracked?
>>>
>>> Something else I noticed is that they have raised the amperage rating on the
>>> 30A disconncect per pole by 2 amps from 18 to 20 which is good especially
>>> when using higher amperage modules like Evergreen ES-A series which would
>>> not have ben allowed to use the 30A disconnect as the short circuit current
>>> rating was too high for the derated poles.
>>>
>>> This is not a huge concern as more and more of the inverters we are using
>>> these days have an appropriate disconnect included with the inverter
>>> negating the need for an additional stand alone disconnect.
>>>
>>> On a side note............Are there any other manufacturers making listed
>>> muiti pole DC disconnects in which each pole can handle one string? Also
>>> there is definately a need for roof mounted multi string (1-4 strings)
>>> combiner boxes with integrated DC disconnects for residential applications
>>> that have a reasonable price.......any one know if any?
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>
>>
>>
>>
>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
>>
>> Check out participant bios:
>> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>
>>
>>
>>
>>
>>
>>
>> No virus found in this incoming message.
>> Checked by AVG - www.avg.com <http://www.avg.com>
>> Version: 9.0.725 / Virus Database: 270.14.135/2615 - Release Date: 01/11/10
>> 11:35:00
>>
>>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
David Brearley, Senior Technical Editor
SolarPro magazine
NABCEP Certified PV Installer
david.brearley at solarprofessional.com
Direct: 541.261.6545
Fax: 541.512.0343
Visit our Web site at solarprofessional.com
(Sample copy available for download at: solarprofessional.com/sample)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20100111/aa05f3c6/attachment-0001.htm>
More information about the RE-Wrenches
mailing list