[RE-wrenches] Square D DC disconnects
R Ray Walters
ray at solarray.com
Tue Jan 12 01:26:24 EST 2010
I got into that one a few years ago with an inspector.
He cited 110.2.
"Approved" according to article 100 means: acceptable to the AHJ.
So put article 100 into 110.2 and you get:
"Conductors and Equipment required or permitted shall be acceptable only if 'acceptable to the AHJ' "
Basically I call these 2 sections of the code read together as the 'AHJ = The Man' ruling.
I guess there was some politics involved in NOT putting that together for all to see?
R. Walters
ray at solarray.com
Solar Engineer
On Jan 11, 2010, at 5:27 PM, Kent Osterberg wrote:
> David,
>
> The NEC doesn't require UL listing. The most appropriate section of the code about this is Article 110, Requirements for Electrical Installations, it requires equipment to be approved.
More information about the RE-Wrenches