Wrenches:

I have a customer that has a problem with a new generator.  He has two 
VFX3648 inverters in Outback stacking.  He acquired a new generator, a 
Kohler 12RES, a reputable make and model.  Below is a description of the 
problem:

The 12RES seems to be operating OK except for one problem.  At the end of a 
charging cycle, when the gen automatically shuts down and load goes back to 
the inverters, all lights, TVs, etc., flash, one TV shuts off, and a GFI 
trips.  This has happened every time.  It did not happen with the 15RES or 
the smaller back-up gen (which was disconnected manually).  With the 15RES 
the same GFI would occasionally trip while the unit was charging and 
handling house load, but never at the auto shutdown point.  I replaced the 
GFI, but it still trips.  There are three GFIs in the house, but only 
one--always the same--trips.


I suggested he adjust the AC2/Gen transfer delay to a lower number.  He 
reduced it to minimum and this did not resolve the problem.  I also had him 
verify that the AC source is selected as generator, which it is.

Do you have any suggestions?

Thanks in advance,

William Miller