I have a customer that has a problem with a new generator.&nbsp; He has
two VFX3648 inverters in Outback stacking.&nbsp; He acquired a new
generator, a Kohler 12RES, a reputable make and model.&nbsp; Below is a
description of the problem:<br><br>
</font><font face="arial" size=2><i>The 12RES seems to be operating OK
except for one problem.&nbsp; At the end of a charging cycle, when the
gen automatically shuts down and load goes back to the inverters, all
lights, TVs, etc., flash, one TV shuts off, and a GFI trips.&nbsp; This
has happened every time.&nbsp; It did not happen with the 15RES or the
smaller back-up gen (which was disconnected manually).&nbsp; With the
15RES the same GFI would occasionally trip while the unit was charging
and handling house load, but never at the auto shutdown point.&nbsp; I
replaced the GFI, but it still trips.&nbsp; There are three GFIs in the
house, but only one--always the same--trips.<br><br>
<br>
</i></font><font size=3>I suggested he adjust the AC2/Gen transfer delay
to a lower number.&nbsp; He reduced it to minimum and this did not
resolve the problem.&nbsp; I also had him verify that the AC source is
selected as generator, which it is.<br><br>
Do you have any suggestions?<br><br>
Thanks in advance,<br><br>
William Miller<br><br>
<br>
<x-sigsep><p></x-sigsep>
<u>Please note new e-mail address and domain:<br><br>
</u>William Miller <br>
Miller Solar<br>
Voice :805-438-5600<br>
email: william@millersolar.com<br>
<a href="http://millersolar.com/" eudora="autourl">http://millersolar.com<br>
</a>License No. C-10-773985<br>
</font></body>