[RE-wrenches] wire gauge reducers

William Miller william at millersolar.com
Tue Sep 22 00:29:20 EDT 2009


Colleagues:

There is no shame in referring to these devices as reducers.  As long as 
the smallest conductor size meets ampacity and voltage drop ratings, the 
use of larger copper is something to be proud of.  It indicates an 
awareness of efficiency through design.

We don't favor splices that are not secured to a mounting surface.  We want 
to be able to access a conductor for testing and labelling and we want to 
know where it is in a given enclosure.  Therefore we use power distribution 
blocks such as those manufactured by Greaves, Ilsco and Square D.  Here is 
a link to Illsco:  http://tinyurl.com/l6msc6

This links shows these in the 
field: 
http://millersolar.com/Portfolio/Inverters/battery_iinverters/GH_FX/GH_Outback.html

William Miller





At 07:17 PM 9/21/2009, you wrote:


>Hi Karpal,
>
>Insulated Cable Terminal Blocks, like the ones made by Polaris and others, 
>work really well.
>
>Polaris: 
><http://www.polarisconnectors.com/fine_stranded_grey.html>http://www.polarisconnectors.com/fine_stranded_grey.html
>
>Or Ilsco: 
><http://www.ilsco.com/productcategory.aspx?akjdjfv=bq9oHViFaxQnf2g6uRehNA%3d%3d&kfnejkf=PQ4y9C2vFEtL0I9NN25RaXTu7nvvtfQWhY2ly2ShYpg%3d>http://www.ilsco.com/productcategory.aspx?akjdjfv=bq9oHViFaxQnf2g6uRehNA%3d%3d&kfnejkf=PQ4y9C2vFEtL0I9NN25RaXTu7nvvtfQWhY2ly2ShYpg%3d
>
>Or, you can also use a splicer right at the inverter terminals:
>
><http://www.ilsco.com/ProductsDetail.aspx?kfjkff=uE1VYYLG5SoDpPlUKKAJeg%3d%3d&fjjfhjhj=H5Hi3ZmGXgnPYbyoSlyg192pVV62SE3BAZmhQMpx%2bq0%3d>http://www.ilsco.com/ProductsDetail.aspx?kfjkff=uE1VYYLG5SoDpPlUKKAJeg%3d%3d&fjjfhjhj=H5Hi3ZmGXgnPYbyoSlyg192pVV62SE3BAZmhQMpx%2bq0%3d
>
>
>Brian Teitelbaum
>AEE Solar
>
>From: re-wrenches-bounces at lists.re-wrenches.org 
>[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Kirpal Khalsa
>Sent: Monday, September 21, 2009 4:56 PM
>To: RE-wrenches
>Subject: [RE-wrenches] wire gauge reducers
>
>Hi all.....anyone have any recommendations for good lugs useful as 
><http://www.google.com/search?hl=en&ei=ARG4SvuoOJKAswPmwogb&sa=X&oi=spell&resnum=0&ct=result&cd=1&q=wire+gauge+reducers&spell=1>wire 
>gauge<http://www.google.com/search?hl=en&ei=ARG4SvuoOJKAswPmwogb&sa=X&oi=spell&resnum=0&ct=result&cd=1&q=wire+gauge+reducers&spell=1> 
>reducers?
>we need to go from #4AWG to #6AWG in the terminals.......specifically we 
>are trying to land our wires in the SMA DC Disconnect which handles a 
>maximum of #6AWG wire size.....
>I was hoping for some ideas other than butt connectors......
>Thanks!!!
>--
>Sunny Regards,
>Kirpal Khalsa
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20090921/295f898a/attachment-0001.htm>


More information about the RE-Wrenches mailing list