<font size=3>Colleagues:<br><br>
There is no shame in referring to these devices as reducers.&nbsp; As
long as the smallest conductor size meets ampacity and voltage drop
ratings, the use of larger copper is something to be proud of.&nbsp; It
indicates an awareness of efficiency through design.<br><br>
We don't favor splices that are not secured to a mounting surface.&nbsp;
We want to be able to access a conductor for testing and labelling and we
want to know where it is in a given enclosure.&nbsp; Therefore we use
power distribution blocks such as those manufactured by Greaves, Ilsco
and Square D.&nbsp; Here is a link to Illsco:&nbsp;
<a href="http://tinyurl.com/l6msc6" eudora="autourl"><b>http://tinyurl.com/l6msc6</a></b>
<br><br>
This links shows these in the field:&nbsp; <a href="http://millersolar.com/Portfolio/Inverters/battery_iinverters/GH_FX/GH_Outback.html" eudora="autourl">http://millersolar.com/Portfolio/Inverters/battery_iinverters/GH_FX/GH_Outback.html</a><br><br>
William Miller<br><br>
<br><br>
<br><br>
At 07:17 PM 9/21/2009, you wrote:<br><br>
<br>
<blockquote type=cite class=cite cite>Hi Karpal,<br>
&nbsp;<br>
Insulated Cable Terminal Blocks, like the ones made by Polaris and others, work really well.<br>
&nbsp;<br>
Polaris:&nbsp;&nbsp; <a href="http://www.polarisconnectors.com/fine_stranded_grey.html">http://www.polarisconnectors.com/fine_stranded_grey.html</a><br>
&nbsp;<br>
Or Ilsco: <a href="http://www.ilsco.com/productcategory.aspx?akjdjfv=bq9oHViFaxQnf2g6uRehNA%3d%3d&amp;kfnejkf=PQ4y9C2vFEtL0I9NN25RaXTu7nvvtfQWhY2ly2ShYpg%3d">http://www.ilsco.com/productcategory.aspx?akjdjfv=bq9oHViFaxQnf2g6uRehNA%3d%3d&amp;kfnejkf=PQ4y9C2vFEtL0I9NN25RaXTu7nvvtfQWhY2ly2ShYpg%3d</a><br>
&nbsp;<br>
Or, you can also use a splicer right at the inverter terminals:<br>
&nbsp;<br>
<a href="http://www.ilsco.com/ProductsDetail.aspx?kfjkff=uE1VYYLG5SoDpPlUKKAJeg%3d%3d&amp;fjjfhjhj=H5Hi3ZmGXgnPYbyoSlyg192pVV62SE3BAZmhQMpx%2bq0%3d">http://www.ilsco.com/ProductsDetail.aspx?kfjkff=uE1VYYLG5SoDpPlUKKAJeg%3d%3d&amp;fjjfhjhj=H5Hi3ZmGXgnPYbyoSlyg192pVV62SE3BAZmhQMpx%2bq0%3d</a><br>
&nbsp;<br>
&nbsp;<br>
Brian Teitelbaum<br>
AEE Solar<br>
&nbsp;<br>
<b>From:</b> re-wrenches-bounces@lists.re-wrenches.org [<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" eudora="autourl">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>] <b>On Behalf Of </b>Kirpal Khalsa<br>
<b>Sent:</b> Monday, September 21, 2009 4:56 PM<br>
<b>To:</b> RE-wrenches<br>
<b>Subject:</b> [RE-wrenches] wire gauge reducers<br>
&nbsp;<br>
Hi all.....anyone have any recommendations for good lugs useful as<u> <a href="http://www.google.com/search?hl=en&amp;ei=ARG4SvuoOJKAswPmwogb&amp;sa=X&amp;oi=spell&amp;resnum=0&amp;ct=result&amp;cd=1&amp;q=wire+gauge+reducers&amp;spell=1">wire </a><b><i>gauge</i></b><a href="http://www.google.com/search?hl=en&amp;ei=ARG4SvuoOJKAswPmwogb&amp;sa=X&amp;oi=spell&amp;resnum=0&amp;ct=result&amp;cd=1&amp;q=wire+gauge+reducers&amp;spell=1"> reducers</a></u>?<br>
we need to go from #4AWG to #6AWG in the terminals.......specifically we are trying to land our wires in the SMA DC Disconnect which handles a maximum of #6AWG wire size.....<br>
I was hoping for some ideas other than butt connectors......<br>
Thanks!!!<br>