[RE-wrenches] Magnum inverters (not really a power factor issue)
Travis Creswell
tcreswell at ozarkenergyservices.com
Mon Aug 3 15:27:37 EDT 2009
I've found that well pumps have their own set of strange rules. I'm talking
twilight zone stuff. For example we wrenches talk about 2 wire and 3 wire
pumps but around here the suppliers and well service people talk about 240
(two wire, I suppose) and 230 (3 wire) pumps. Both of them a 240 single
phase in my book.
We've had some very odd experiences and are currently in the middle of
another one. We have a pump that won't drop the start windings and
overloads the pumps controller (not the inverter or the breaker). Does it
both on the dual 4kW inverter and the 12kW generator so it's not a power
thing. This happened a few years ago at another customer with a different
pump brand and inverter. It took out 2 sets of Outback Boards and caused us
no end of aggravation. Might pump for a few seconds then overload the
inverter or might work fine for weeks then trip the control box. Swapped
out the pump and down pipe wire and things were fine but no one, not even
the well pump experts could help us figure it out. Normally they work great
but when they don't they can drive you crazy.
Travis Creswell
Ozark Energy Services
_____
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Matt Tritt
Sent: Monday, August 03, 2009 12:44 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Magnum inverters (not really a power factor
issue)
I'm hoping that it WILL be embarrassingly simple! I'm glad this wasn't
something I installed since you all know what it's like to find errors is
someone else's work. ;-)
Matt
dan at foxfire-energy.com wrote:
Boy, This reminds me of a problem I had a few years ago -- don't remember
the particulars, except that it was embarrassingly simple -- like a missing
connection or something. db
Dan Brown
President
Foxfire Energy Corp.
Renewable Energy Systems
(802)-483-2564
www.Foxfire-Energy.com
NABCEP #092907-44
-------- Original Message --------
Subject: Re: [RE-wrenches] Magnum inverters (not really a power factor
issue)
From: boB Gudgel <mailto:boB at midnitesolar.com> <boB at midnitesolar.com>
Date: Sun, August 02, 2009 12:53 am
To: RE-wrenches <mailto:re-wrenches at lists.re-wrenches.org>
<re-wrenches at lists.re-wrenches.org>
Darryl Thayer wrote:
> The 120 leg to leg, that is strange. Is it possible the Inverter has an
output not split phase? perhaps 2 phase or 4 phase? giving the phase to
neutral a normal value and the phase to phase a weird value? I do not think
thy would build it this way.
>
>
Matt said:
"When I checked phase to phase I also only got 120"
OK, Matt, that part passed right through me... Hmmmm.... (60 Hz
Hmmmm... too)
boB
> --- On Sat, 8/1/09, Matt Tritt <mailto:solarone at charter.net>
<solarone at charter.net> wrote:
>
>
>> From: Matt Tritt <mailto:solarone at charter.net> <solarone at charter.net>
>> Subject: Re: [RE-wrenches] Magnum inverters (not really a power factor
issue)
>> To: "RE-wrenches" <mailto:re-wrenches at lists.re-wrenches.org>
<re-wrenches at lists.re-wrenches.org>
>> Date: Saturday, August 1, 2009, 10:43 PM
>>
>>
>>
>>
>>
>>
>> The next time I'm up there I'll take another tech
>> with me, plenty of
>> meters and go through every DC and AC connection (they all
>> looked good
>> first time around) to try and get to the bottom of the
>> problem prior to
>> taking a harder look at Magnum. I have to say, though, that
>> I have
>> heard a couple of comments that tend to suggest that the
>> inverter might
>> turn out to be one logical place to look. I like these
>> inverters a lot,
>> and I really hope that we find some other issue.
>>
>>
>>
>> To replay the symptoms, there is no audible or visual (as
>> in motor
>> starter noises or dimming light) indication that the pump
>> is attempting
>> to do anything other than sit there when inverter voltage
>> is connected
>> to it. When the genny power is applied, there is a
>> discernable working
>> under a load sound from the engine, and the pump works. I
>> only had the
>> homeowner's lousy dime store anaglog meter to work
>> with, but the
>> voltage from the inverter was right on 120 volts per leg.
>> When I
>> checked phase to phase I also only got 120 - that's
>> kind of weird, but
>> it might simply be the meter. All the household loads run
>> flawlessly
>> (but this is a pretty fundamental cabin, so the TV and DVD
>> player are
>> the most exotic things plugged in. The run to the pump is
>> adequately
>> sized - - - - - in other words, it all seems run of the
>> mill, except
>> that the pump only ran successfully one time and not on any
>> further
>> attempts. Golly..
>>
>>
>>
>> Matt
>>
>>
>>
>> boB Gudgel wrote:
>> Larry
>> Crutcher, Starlight Solar wrote:
>>
>>
>> Hey Matt,
>>
>> I sure wish their techie's would get to the bottom of
>> it. I am getting
>> gun-shy about selling Magnum and they are about the best
>> available for
>> small 12 volt systems. I have spend hours trying to solve
>> the problem.
>> My customer is still not a happy camper.
>>
>>
>>
>>
>> Larry Crutcher
>>
>>
>> Starlight Solar
>>
>>
>> (928) 941-1660
>>
>>
>> Renewable Energy Products, Service and Installation
>>
>>
>>
>>
>>
>> Can you get someone to look at the voltage and/or current
>> going into
>> that pump ?? Scope ? Meter ?
>> Even a
>>
>>
>> power factor meter would have both voltage and current
>> measurements.
>> Some even have a mediocre scope built in.
>>
>>
>> A scope AND a meter is best of course.
>>
>>
>>
>>
>> Need stats. AC an DC side. AC voltage at
>> the pump and at the
>> inverter.
>>
>>
>>
>>
>> Must have more information. Yes, it
>> ~could~ be a Magnum inverter
>> issue, but need more information other than "it
>> doesn't work"
>>
>>
>>
>>
>> Does the voltage dip when the pump tries to start ?
>> What is the
>> maximum Ac and DC current ? Most basic info for
>> troubleshooting.
>>
>>
>>
>>
>> The inverter manufacturer can probably help somewhat if
>> they have this
>> info.
>>
>>
>>
>>
>> Just a suggestion here.
>>
>>
>>
>>
>> boB
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>> On Aug 1, 2009, at 4:28 PM, Matt Tritt wrote:
>>
>>
>>
>>
>> I took boB's advice and
>> talked to Magnum
>> about the problem. Their take on it? "Hmmm, beats
>> me!" I might be
>> paraphrasing, but that's the drift. All in all, I'd
>> say that the
>> suggestions from the group are at least as good as the
>> one's from the
>> manufacturer.
>>
>>
>>
>>
>> Matt T
>>
>>
>>
>>
>> Larry Crutcher, Starlight Solar wrote:
>>
>>
>> Don't forget, this is a
>> Magnum inverter
>> and Magnum has issues. I have two customers with
>> Magnum problems. One
>> is a washer that will work perfectly on a cheap
>> import inverter; the
>> other has a Vizio TV that works fine on shore power
>> and generator.
>> Soooo...maybe there are pumps and other items that
>> are anti-Magnum.
>>
>>
>>
>>
>>
>>
>> Larry Crutcher
>>
>>
>> Starlight Solar
>>
>>
>> (928) 941-1660
>>
>>
>> Renewable Energy Products, Service and Installation
>>
>>
>>
>>
>>
>>
>> ------------------------------------------------------------------------
>>
>>
>>
>>
>> _______________________________________________
>>
>>
>> List sponsored by Home Power magazine
>>
>>
>>
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>>
>>
>>
>> Options & settings:
>>
>>
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>
>>
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>>
>>
>>
>> List rules & etiquette:
>>
>>
>> www.re-wrenches.org/etiquette.htm
>>
>>
>>
>>
>> Check out participant bios:
>>
>>
>> www.members.re-wrenches.org
>>
>>
>>
>>
>>
>>
>>
>> _______________________________________________
>>
>>
>> List sponsored by Home Power magazine
>>
>>
>>
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>>
>>
>>
>> Options & settings:
>>
>>
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>
>>
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>>
>>
>>
>> List rules & etiquette:
>>
>>
>> www.re-wrenches.org/etiquette.htm
>>
>>
>>
>>
>> Check out participant bios:
>>
>>
>> www.members.re-wrenches.org
>>
>>
>>
>>
>>
>> No virus found in this incoming message.
>> Checked by AVG - www.avg.com
>> Version: 8.5.392 / Virus Database: 270.13.39/2275 - Release
>> Date: 08/01/09 09:38:00
>>
>>
>>
>>
>>
>>
>> -----Inline Attachment Follows-----
>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_____
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_____
No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 8.5.392 / Virus Database: 270.13.42/2278 - Release Date: 08/02/09
17:56:00
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20090803/78ea6b77/attachment-0001.htm>
More information about the RE-Wrenches
mailing list