Hi Dick,
Thanks for the suggestion. I will run the concept by the SMA tech
people. I did use the SMA spec sheets in sizing the wiring, but
maybe opening the relays creates fault current at a voltage that will
jump the gap.
Drake
At 10:50 PM 6/4/2009, you wrote:
>Hi Drake,
>
>I'm sending you some attachments off list as well.
>They are Sunny Boy Specs from the SMA Installation Manuals,
>which are more complete than those on the SMA data sheets.
>
>Note, the Maximum Output Fault Current for the 3000 & 4000 is 30 amps,
>while Maximum Overcurrent Protection is 30 Amps.
>
>The Maximum Output Fault Current for the 7000 is 57.6 amps, the
>Maximum Overcurrent Protection is 50 amps.
>
>This might be your problem.
>Upsizing the conductors and breakers for the 3000 and 7000 might be a fix.
>SMA tech support could probably shed some light.
>
>Dick
>
>
>
>--- You wrote:
>Hi Dick,
>
>There are three inverters, all Sunny Boys, a 3000, 4000 and a
>7000. The breakers are QO. The AC conductor sizes are #8 for the
>7000, #10 for the 4000 and #12 for the 3000. The breakers are set
>for the NEC ratings of the wire (40 A, 30 A and 20 A.).
>
>I sent some information to you off the list with some attachments.
>
>Drake
>--- end of quote ---
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
NABCEP Certified PV Installer TM
Office - 740-448-7328
Mobile - 740-856-9648
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20090605/098d35f0/attachment-0001.htm>
More information about the RE-Wrenches
mailing list