Hi Dick,<br><br>
Thanks for the suggestion. I will run the concept by the SMA tech
people.&nbsp; I did use the SMA spec sheets in sizing the wiring, but
maybe opening the relays creates fault current at a voltage that will
jump the gap.<br><br>
Drake <br><br>
At 10:50 PM 6/4/2009, you wrote:<br>
<blockquote type=cite class=cite cite="">Hi Drake,<br><br>
I'm sending you some attachments off list as well.<br>
They are Sunny Boy Specs from the SMA Installation Manuals, <br>
which are more complete than those on the SMA data sheets.<br><br>
Note, the Maximum Output Fault Current for the 3000 &amp; 4000 is 30
amps, <br>
while Maximum Overcurrent Protection is 30 Amps.<br><br>
The Maximum Output Fault Current for the 7000 is 57.6 amps, the<br>
Maximum Overcurrent Protection is 50 amps.<br><br>
This might be your problem.<br>
Upsizing the conductors and breakers for the 3000 and 7000 might be a
fix.<br>
SMA tech support could probably shed some light.<br><br>
Dick<br><br>
<br><br>
--- You wrote:<br>
Hi Dick,<br><br>
There are three inverters, all Sunny Boys, a 3000, 4000 and a <br>
7000.&nbsp; The breakers are QO.&nbsp; The AC conductor sizes are #8 for
the <br>
7000, #10 for the 4000 and #12 for the 3000.&nbsp; The breakers are set
<br>
for the NEC ratings of the wire (40 A, 30 A and 20 A.).<br><br>
I sent some information to you off the list with some
attachments.<br><br>
Drake<br>
--- end of quote ---<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Options &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">
www.re-wrenches.org/etiquette.htm</a><br><br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">
www.members.re-wrenches.org</a></blockquote>
<x-sigsep><p></x-sigsep>
<font color="#0000FF">Drake Chamberlin<br>
Athens Electric<br>
OH License 44810<br>
CO License 3773<br>
NABCEP Certified PV Installer </font><font size=1 color="#0000FF">TM<br>
</font><font color="#0000FF">Office - 740-448-7328<br>
Mobile - 740-856-9648 </font></body>