[RE-wrenches] AC coupled relay

Drake Chamberlin drake.chamberlin at redwoodalliance.org
Thu Jun 4 22:33:31 EDT 2009


Hi Dick,

There are three inverters, all Sunny Boys, a 3000, 4000 and a 
7000.  The breakers are QO.  The AC conductor sizes are #8 for the 
7000, #10 for the 4000 and #12 for the 3000.  The breakers are set 
for the NEC ratings of the wire (40 A, 30 A and 20 A.).

I sent some information to you off the list with some attachments.

Drake




At 08:54 PM 6/4/2009, you wrote:
>Hi Drake,
>
>Could you please provide more information,
>array size, inverter make / model, conductor size,
>breaker rating, breaker brand?
>
>Dick
>Solarwind Electric
>Bradford, VT
>
>
>--- You wrote:
>If I'm following this thread correctly,  the
>relay is to break the flow of AC current to the
>battery based inverter (Outback) from a direct
>grid tie inverter when the grid is down and the
>batteries are full.  The AC coupling here would
>be done at the protected loads panel, fed from the AC Out of the Outback.
>
>We are having problems breaking the AC from
>direct grid tie inverters feeding directly into
>the grid.  When the relays open, the breakers
>that the inverters feed into, trip.  They don't
>always trip, but trip randomly.
>
>The relays are open frame, similar to the ones
>you describe below.  Why are we having this
>problem, as it seems that what we are doing is common practice?
>
>Thanks for your help.
>
>Drake
>--- end of quote ---
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org

Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
NABCEP Certified PV Installer TM
Office - 740-448-7328
Mobile - 740-856-9648  
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20090604/069ca440/attachment-0001.htm>


More information about the RE-Wrenches mailing list