Hi Dick,<br><br>
There are three inverters, all Sunny Boys, a 3000, 4000 and a 7000.&nbsp;
The breakers are QO.&nbsp; The AC conductor sizes are #8 for the 7000,
#10 for the 4000 and #12 for the 3000.&nbsp; The breakers are set for the
NEC ratings of the wire (40 A, 30 A and 20 A.).&nbsp;&nbsp; <br><br>
I sent some information to you off the list with some
attachments.<br><br>
Drake <br><br>
<br><br>
<br>
At 08:54 PM 6/4/2009, you wrote:<br>
<blockquote type=cite class=cite cite="">Hi Drake,<br><br>
Could you please provide more information, <br>
array size, inverter make / model, conductor size, <br>
breaker rating, breaker brand?<br><br>
Dick <br>
Solarwind Electric<br>
Bradford, VT<br><br>
<br>
--- You wrote:<br>
If I'm following this thread correctly,&nbsp; the <br>
relay is to break the flow of AC current to the <br>
battery based inverter (Outback) from a direct <br>
grid tie inverter when the grid is down and the <br>
batteries are full.&nbsp; The AC coupling here would <br>
be done at the protected loads panel, fed from the AC Out of the
Outback.<br><br>
We are having problems breaking the AC from <br>
direct grid tie inverters feeding directly into <br>
the grid.&nbsp; When the relays open, the breakers <br>
that the inverters feed into, trip.&nbsp; They don't <br>
always trip, but trip randomly.<br><br>
The relays are open frame, similar to the ones <br>
you describe below.&nbsp; Why are we having this <br>
problem, as it seems that what we are doing is common practice?<br><br>
Thanks for your help.<br><br>
Drake<br>
--- end of quote ---<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Options &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">
www.re-wrenches.org/etiquette.htm</a><br><br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">
www.members.re-wrenches.org</a></blockquote>
<x-sigsep><p></x-sigsep>
<font color="#0000FF">Drake Chamberlin<br>
Athens Electric<br>
OH License 44810<br>
CO License 3773<br>
NABCEP Certified PV Installer </font><font size=1 color="#0000FF">TM<br>
</font><font color="#0000FF">Office - 740-448-7328<br>
Mobile - 740-856-9648 </font></body>
</html>