Drake:

Sorry again, but this is still not clear.  Questions below in red (could 
you draft a block diagram and post it?):

At 03:56 PM 7/30/2008, Drake Chamberlin wrote:

>>2. The commercial building has a service that you will not feed the 
>>grid-tie to.
>
>Yes.  It also has its own service.  The commercial building gets some 
>solar also.  The tax benefits would be for it all to be on the commercial 
>service, but we are following the owner's request.

According to the two paragraphs above, the commercial building has two 
commercial services???  One will receive PV and one will not??


>>3. This commercial building has a "feed-through" breaker panel that was 
>>installed for the PV to tie to.  This "Feed-through" box does not connect 
>>to the commercial service.
>
>Yes
>
>>Where is the service that the PV system would feed?  In a separate building?
>
>Yes, in the residence on the property.  The meter is on the commercial 
>building.

Referring to the passage above:  I have learned that in most cases, the 
service and the meter are the same device.  Are you telling me the legal 
service is separate from the meter???


>>Where does the feeder connected to the bottom of this "Feed-through" 
>>panel go?
>
>
>
>It goes to the residence, which is another building on the same property.