<html>
<body>
Drake:<br><br>
Sorry again, but this is still not clear.&nbsp; Questions below in
<font color="#FF0000">red (could you draft a block diagram and post
it?):<br><br>
</font>At 03:56 PM 7/30/2008, Drake Chamberlin wrote:<br><br>
<blockquote type=cite class=cite cite><blockquote type=cite class=cite cite>2.
The commercial building has a service that you will not feed the grid-tie
to.</blockquote><br>
Yes.&nbsp; It also has its own service.&nbsp; The commercial building
gets some solar also.&nbsp; The tax benefits would be for it all to be on
the commercial service, but we are following the owner's request.<br>
</blockquote><br>
<font color="#FF0000">According to the two paragraphs above, the
commercial building has two commercial services???&nbsp; One will receive
PV and one will not??<br><br>
<br>
</font><blockquote type=cite class=cite cite><blockquote type=cite class=cite cite>3.
This commercial building has a &quot;feed-through&quot; breaker panel
that was installed for the PV to tie to.&nbsp; This
&quot;Feed-through&quot; box does not connect to the commercial
service.</blockquote><br>
Yes<br><br>
<blockquote type=cite class=cite cite>Where is the service that the PV
system would feed?&nbsp; In a separate building?</blockquote><br>
Yes, in the residence on the property.&nbsp; The meter is on the
commercial building.<br>
</blockquote><br>
<font color="#FF0000">Referring to the passage above:&nbsp; I have
learned that in most cases, the service and the meter are the same
device.&nbsp; Are you telling me the legal service is separate from the
meter???<br><br>
<br>
</font><blockquote type=cite class=cite cite><blockquote type=cite class=cite cite>Where
does the feeder connected to the bottom of this &quot;Feed-through&quot;
panel go?</blockquote><br><br>
<br>
It goes to the residence, which is another building on the same
property.<br>
<blockquote type=cite class=cite cite></blockquote></blockquote></body>