Dick,
After reading through Article 230 again, I think I agree with your
assessment that there is a single service and multiple service disconnects
when we connect to the supply side of the service disconnect. I also agree
with your assessment that Article 230 is referring to a total service
capacity and does not limit the minimum of individual service connections.
Article 230 also uses the term "tap", but this is confusing and potentially
dangerous. The "tap rule", commonly referred to in Article 240 only applies
to circuits downstream of the service disconnect and overcurrent protection.
I'm constantly learning and appreciate your insight into the NEC. There is
so much to know and understand about the code, and I want to make sure the
aspects of the code that affect PV systems are understood by myself first
and by those I teach. I will make a point to correct my reference to line
side service connections (and still avoid the confusing term "tap").
If there is any way you can find the time and finances to make it to our
June 5-6 meeting in Golden, Colorado, we could certainly use your input.
Please contact me offline to discuss your involvement at 707-332-0761.
Bill.
-----Original Message-----
From: Dick Ratico [mailto:Richard.L.Ratico at VALLEY.NET]
Sent: Saturday, May 03, 2008 5:58 PM
To: RE-wrenches at topica.com
Subject: RE: point of connection [RE-wrenches]
Bill, William, & Esteemed Wrenches,
In the otherwise well written document by John Wiles, cited by Bill, I
believe
John is in error when he says, "Section 230.79(D) requires that the
disconnect
have a minimum rating of 60 amps.
Here's the url, compliments of William: http://www.nmsu.edu/~tdi/pdf-
resources/IAEI-1to2-06.pdf
John is talking about the PV disconnect. In this instance, the PV disconnect
is
only PART of the total service disconnect. It is but one switch of up to six
allowed per service. Article 230.79 specifies the minimum size of the entire
service not of the individual switches.
Respectfully,
Dick Ratico
Solarwind Electric
${bottom_text_ad}
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: ${recipient}
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.${encoded_sub_id}.${EMC}
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?pXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list