PV Grounding [RE-wrenches]
Ray Walters
walters at taosnet.com
Tue Apr 15 23:32:26 EDT 2008
<x-flowed>
WE use a braided, plated copper ground strap (Anixter) that is about
8 ga equivalent. It is what I saw being used on a commercial tracking
system over 20 years ago, and its all we use for exposed module
grounding.
IMHO, using THHN outside is not only not NEC, but is just bad
practice. I know its not a current carrying conductor, and doesn't
need the insulation, but I've seen plenty of it cracking and peeling.
Looks like crap.
There's that little thing in the code (110.12) "Electrical equipment
shall be installed in a neat and workmanlike manner"
Without the insulation, stranded 10 ga isn't allowed for exposed
locations. see 250.64 B
THe real solution is allowing products like the WEEB grounding system
and use the mounting frame itself as the grounding conductor.
Commercial buildings allow the steel structure to be the grounding
conductor, on arrays its just a matter of dealing with the aluminum
to steel galvanic reaction issues, and then getting the inspector to
sign off on it.
Ray Walters
On Apr 15, 2008, at 6:42 PM, Mark Frye wrote:
>
> I have taken to using 8# bare stranded from module all the way
> through to
> the point of connection at the ac system GEC.
>
> i too have heard of folks disallowing the #10 GRN STD as a PV
> equipment
> ground, something about the insulation is not rated for UV exposure or
> extreme current during lighting strike, but.....who needs
> insulation on an
> equipment ground? (isolated ground systems being a separate issue)
>
> Would definently be interest in a good explanation why this should be
> disallowed.
>
> Mark Frye
> Berkeley Solar Electric Systems
> 271 Vistamont Dr
> Grass Valley CA 95945
> (530) 401-8024
> www.berkeleysolar.com
>
> -----Original Message-----
> From: Peter Parrish [mailto:peter.parrish at calsolareng.com]
> Sent: Tuesday, April 15, 2008 5:31 PM
> To: RE-wrenches at topica.com
> Subject: PV Grounding [RE-wrenches]
>
>
> After all these years I must confess I was stymied by the comment of a
> self-styled expert on grounding. He said that grounding of roof
> mounted PV
> modules cannot be accomplished with stranded wire -- period. We were
> discussing 10 AWG, 19 strands vs 10 AWG solid, so I didn't venture
> beyond
> the case at hand.
>
> We normally use 10 AWG solid but occasionally we run out and use 10
> AWG THHN
> Green 19 strand in a pinch (module to module, rail to rail or sub-
> array to
> sub-array)
>
> For the record, the PV modules had a series fuse rating of 15A and
> we were
> paralleling two strings at the inverter, which was a Xantrex GT4.0
> with a
> 600 volt 1-Amp ground fault protection fuse.
>
> Is he right?
>
> - Peter
>
> California Solar Engineering, Inc.
> CA Lic. 854779, NABCEP Cert. 031806-26
> peter.parrish at calsolareng.com
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://lists.topica.com/lists/RE-
> wrenches/read
>
> List rules & how to change your email address: www.mrsharkey.com/
> wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
>
R. Walters
Solarray.com
NABCEP # 04170442
--
[Non-text portions of this message have been removed]
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list