PV Grounding [RE-wrenches]
Mark Frye
markf at berkeleysolar.com
Tue Apr 15 20:42:44 EDT 2008
I have taken to using 8# bare stranded from module all the way through to
the point of connection at the ac system GEC.
i too have heard of folks disallowing the #10 GRN STD as a PV equipment
ground, something about the insulation is not rated for UV exposure or
extreme current during lighting strike, but.....who needs insulation on an
equipment ground? (isolated ground systems being a separate issue)
Would definently be interest in a good explanation why this should be
disallowed.
Mark Frye
Berkeley Solar Electric Systems
271 Vistamont Dr
Grass Valley CA 95945
(530) 401-8024
www.berkeleysolar.com
-----Original Message-----
From: Peter Parrish [mailto:peter.parrish at calsolareng.com]
Sent: Tuesday, April 15, 2008 5:31 PM
To: RE-wrenches at topica.com
Subject: PV Grounding [RE-wrenches]
After all these years I must confess I was stymied by the comment of a
self-styled expert on grounding. He said that grounding of roof mounted PV
modules cannot be accomplished with stranded wire -- period. We were
discussing 10 AWG, 19 strands vs 10 AWG solid, so I didn't venture beyond
the case at hand.
We normally use 10 AWG solid but occasionally we run out and use 10 AWG THHN
Green 19 strand in a pinch (module to module, rail to rail or sub-array to
sub-array)
For the record, the PV modules had a series fuse rating of 15A and we were
paralleling two strings at the inverter, which was a Xantrex GT4.0 with a
600 volt 1-Amp ground fault protection fuse.
Is he right?
- Peter
California Solar Engineering, Inc.
CA Lic. 854779, NABCEP Cert. 031806-26
peter.parrish at calsolareng.com
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list