Larry/Wrenches:
Your concern regarding balancing of the solar resource is certainly
valid.
You can only estimate the loads so closely and even then you will never
get it perfectly right.
You can help to balance the generation side by using the programmable
control relays in the Sunny Islands.
For example you can program one of the relays to close when you reach a
specific state of charge or when the battery goes into absorption phase.
You would then use one (or more) external power relays to transfer the
output of the Sunny Boy from one cluster to another. This helps to
balance the solar resource across the various clusters and maximize the
use of the solar resource. I do not have a diagram of this yet but we
hope to have several applications notes regarding the use of the control
relays completed after the first of the year.
If I understand your comment regarding bypassing of the sub-panels back
to the generator it should still be possible to do this using multiple
smaller bypass switches one for each sub panel rather than a single
large bypass switch.
Best Regards,
John Berdner
>>> larry at starlightsolar.com 11/30/2007 09:27:06 AM >>>
Thank you John. My main concern with not having a common battery bank
is
the distribution of the PV resource. Obviously I want to use all of the
PV, all the time. With 4 clusters on this system, would it be better to
use SB grid tie inverters instead of splitting up the PV into 4
charging
systems? Would this allow the SI's to better balance the charging of
the
4 banks or would your description below be more efficient? Do you have
a
diagram showing the relay configuration? I don't see anything in the
manual about this.
In this system all 3-phase sets will be paralleled. I do not think we
can break up the AC distribution into sub panels because the owner
wants
to be able to bypass back to the generator. I will look at this further
though.
Thank you,
Larry Crutcher
Starlight Solar
John
--
[Non-text portions of this message have been removed]
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list