SMA Sunny Island three phase multi clustering [RE-wrenches]
Larry Crutcher, Starlight Solar
larry at starlightsolar.com
Fri Nov 30 12:27:06 EST 2007
Thank you John. My main concern with not having a common battery bank is
the distribution of the PV resource. Obviously I want to use all of the
PV, all the time. With 4 clusters on this system, would it be better to
use SB grid tie inverters instead of splitting up the PV into 4 charging
systems? Would this allow the SI's to better balance the charging of the
4 banks or would your description below be more efficient? Do you have a
diagram showing the relay configuration? I don't see anything in the
manual about this.
In this system all 3-phase sets will be paralleled. I do not think we
can break up the AC distribution into sub panels because the owner wants
to be able to bypass back to the generator. I will look at this further
though.
Thank you,
Larry Crutcher
Starlight Solar
John Berdner wrote:
......It is also possible to
> switch some of the Sunny Boy power between clusters based on state of
> charge using the programmable relays in the Sunny Island =. This helps
> to balance the solar resource between imbalanced loads on the different
> clusters.
>
> Best Regards,
>
> John Berdner
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list