Feeder sizing [RE-wrenches]
Jim Easton
jeaston at ucsd.edu
Wed Jul 18 01:04:19 EDT 2007
<x-flowed>
I would agree with Bill on the 6 inverters.
Simply adding the power for the seventh is not quite correct because of the
phase angle & unbalance, but I would agree that 200A is sufficient.
(I got 185A for the required ampacity on the two legs with the extra
inverter.)
Jim Easton, PE
(E 11974)
4364 Bonita Road, No. 166
Bonita, CA 91902-1421
Tel: 858-527-0240
Fax: 619-470-861
----- Original Message -----
From: "Keith Cronin" <kcronin at islandenergy.net>
To: <RE-wrenches at topica.com>
Sent: Tuesday, July 17, 2007 5:12 PM
Subject: Feeder sizing [RE-wrenches]
> Hi folks
>
> We are working on a project with 7- SMA 7000's @ 208V.
>
> There spec sheets state 34 amps @ 208V. So, 34 amps x 1.25 = 42.5 amps (50
> amp CB).
>
> Since this is a 3 phase service, 42.5 x 7 = 297.5/ 1.73 = 171 amps. So,
> this
> panel that will house the 7- 2P50's should be 200 amp rated?
>
> I spoke to our resident guru, Bill Brooks, and he has a similar view of
> things. Bill said for the sake of simplicity, take 6 inverters x 42.5 =
> 255/1.73 = 147 amps and add in the additional inverter, due to the
> imbalance
> to come up with the feeder size.
>
> Is there anyone who sees it the same or different?
>
> Thanks
>
> Keith Cronin
> President
> Island Energy Solutions Inc.
> 270 Kuulei Rd. Suite 106
> Kailua, HI 96734
> Electrical Lic C-25221
> 808-262-3268 Tel
> 808-263-0338 Fax
> www.islandenergy.net
> <mailto:kcronin at islandenergy.net> kcronin at islandenergy.net
>
> Disclaimer Statement
>
> The information contained in this communication may be privileged and or
> confidential and is intended only for the use of the recipient's name
> above.
> If the reader of this message is not the intended recipient, you are
> hereby
> notified that any dissemination, distribution, or copying of this
> communication or any of its contents, is strictly prohibited. If received
> in
> error, please return the communication to the sender immediately and
> delete
> the original and any copies from your computer system. Mahalo.
>
>
>
>
> [Non-text portions of this message have been removed]
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
>
>
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list