Feeder sizing [RE-wrenches]

Keith Cronin kcronin at islandenergy.net
Tue Jul 17 20:12:35 EDT 2007



Hi folks

 

We are working on a project with 7- SMA 7000's @ 208V.

 

There spec sheets state 34 amps @ 208V. So, 34 amps x 1.25 = 42.5 amps (50
amp CB).

 

Since this is a 3 phase service, 42.5 x 7 = 297.5/ 1.73 = 171 amps. So, this
panel that will house the 7- 2P50's should be 200 amp rated?

 

I spoke to our resident guru, Bill Brooks, and he has a similar view of
things. Bill said for the sake of simplicity, take 6 inverters x 42.5 =
255/1.73 = 147 amps and add in the additional inverter, due to the imbalance
to come up with the feeder size.

 

Is there anyone who sees it the same or different?

 

Thanks

 

 

Keith Cronin

President

Island Energy Solutions Inc.

270 Kuulei Rd. Suite 106

Kailua, HI 96734

Electrical Lic C-25221

808-262-3268 Tel

808-263-0338 Fax

www.islandenergy.net 

 <mailto:kcronin at islandenergy.net> kcronin at islandenergy.net

 

Disclaimer Statement

The information contained in this communication may be privileged and or
confidential and is intended only for the use of the recipient's name above.
If the reader of this message is not the intended recipient, you are hereby
notified that any dissemination, distribution, or copying of this
communication or any of its contents, is strictly prohibited. If received in
error, please return the communication to the sender immediately and delete
the original and any copies from your computer system. Mahalo.

 


[Non-text portions of this message have been removed]


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: re-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------




More information about the RE-Wrenches mailing list