Drake,
Yes. Regardless of what you call the GEC (DC or AC sep.derived sys). A GEC
from the inverter is currently required and it MUST be connected to the
building grounding electrode system.
Mike Bernhard
----- Original Message -----
From: "Drake Chamberlin" <Drake.Chamberlin at redwoodalliance.org>
To: <RE-wrenches at topica.com>
Sent: Wednesday, June 20, 2007 2:41 PM
Subject: RE: Inverter Output Circuit and DC GEC requirements [RE-wrenches]
>
> Hello Bill,
>
> We recently had an inspector require us to run a GEC to a ground rod from
> a grid tie only system. Usually, this has not been required in systems
> where we don't have batteries and the DC grounding point is internal to
> the inverter. The conductor was only able to make an equipment ground,
> not a connection to the DC grounding.
>
> Is it usually necessary to run a GEC to a rod with grid tie only inverter?
>
> Thanks,
>
> Drake
>
>>If a code inspector requires you to derive a separate ground
>>(690.47(C)(1)),
>>ALWAYS tie that ground to the ac grounding electrode. The bummer to this
>>method is that you must use the larger of the two GECs to run between the
>>two grounding systems (you are creating a grounding electrode system). If
>>you hold off and tie into the ac grounding electrode (690.47(C)(2)), the
>>conductor only has to be sized according to the dc side, which is almost
>>always smaller.
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
>
>
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list