Inverter Output Circuit and DC GEC requirements [RE-wrenches]
Drake Chamberlin
Drake.Chamberlin at redwoodalliance.org
Wed Jun 20 15:41:17 EDT 2007
<x-flowed>
Hello Bill,
We recently had an inspector require us to run a GEC to a ground rod
from a grid tie only system. Usually, this has not been required in
systems where we don't have batteries and the DC grounding point is
internal to the inverter. The conductor was only able to make an
equipment ground, not a connection to the DC grounding.
Is it usually necessary to run a GEC to a rod with grid tie only inverter?
Thanks,
Drake
>If a code inspector requires you to derive a separate ground (690.47(C)(1)),
>ALWAYS tie that ground to the ac grounding electrode. The bummer to this
>method is that you must use the larger of the two GECs to run between the
>two grounding systems (you are creating a grounding electrode system). If
>you hold off and tie into the ac grounding electrode (690.47(C)(2)), the
>conductor only has to be sized according to the dc side, which is almost
>always smaller.
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: re-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list