Advise sought for large off grid PV system; 480 volt 3-phase [RE-wrenches]
Chris Worcester
chris at solarwindworks.com
Sun Apr 1 09:45:20 EDT 2007
Hi Larry,
This might be thinking a little too far outside of the box but here goes.
I've done OutBack 10 packs off grid with 5 tons of lead, nothing in
comparison to where you need to go.
My idea comes from a phone call I had with a potential wind turbine client
in the DC area. He works in a secure building with a large bank of six MW
sized gen sets, and a UPS system with enough lead to support a 2MW (yes
that's megawatt) load draw for 20 Minutes.
Contact APC or Best or one of these large UPS system manufacturers that do
whole skyscraper solutions. Tie in a SMA Sunny Central or equal and you have
an off grid 480V 3phase solution possibly.
Anyone tried this sort of thing?
Sincerely,
Chris Worcester
NABCEP Certified PV Installer TM
USA Distributor of Proven Wind Turbines
Toll Free: 877-682-4503
Fax: 530-582-4603
www.solarwindworks.com
chris at solarwindworks.com
"Proven Energy Solutions"
-----Original Message-----
From: Larry Crutcher [mailto:larry at starlightsolar.com]
Sent: Thursday, March 29, 2007 6:27 PM
To: RE-wrenches at topica.com
Subject: Re: Advise sought for large off grid PV system; 480 volt 3-phase
[RE-wrenches]
Hi Jeff, Thanks for your input. I was told by outback that they can only
support 208/3-phase with one inverter per leg. How can you get 32.4kW?
Since the distribution system is already there and trenching of undisturbed
soil may not be an option, I have to work with what I have. There are six
480 volt transformers ranging from 25 to 117 kva. That can not change
either. If someone made a 480 volt inverter, I would be camping at their
doorstep. I am looking real hard at the Exeltech MX inverters: 60kW,
3-phase, 208. Several people have reassured me (off list) that highly
efficient step-up transformer to make the 480Y will not be a problem;
perhaps 3% loss there.
So far, the design I have will not be paralleling the generator. An isolated
PV/bat/inverter system will take over all loads. The generator will only
operate to support the load demand through high current chargers. A transfer
switch will send loads back to the generator when necessary. The problem
with this, as I see it, is not getting 100% use of the PV. There are only
two circuits leaving the generator building to the village. I could split
this and use the PV for the lesser loads during summer but this could be
problematic.
I really appreciate all the info so far. People on this list are extremely
helpful, kudos to you.
Larry
----- Original Message -----
From: Jeff Oldham
To: RE-wrenches at topica.com
Sent: Thursday, March 29, 2007 2:53 PM
Subject: Re: Advise sought for large off grid PV system; 480 volt 3-phase
[RE-wrenches]
I'm sorry that I don't have more time to go in depth on this, it is indeed
a complex issue that I have and continue to deal with. A few comments -
Transformers can be killer if they mount in numbers much and I've found
wire to be cheaper than tare losses. As a very rough rule of thumb figure on
at least a 3% loss at each transformer and a 1% tare loss 24/7 even without
a load. Large transformers can also give fits to inverters. Gensets have a
limit to a backfeed from inverters and other sources. The rule of thumb on
this one is 30% of genset rating. For your 60kW units this is only 20kW of
PV.
AC coupling gensets w/PV is a tough nut on efficiency, they won't couple
unless the genset is running or you have additional battery based inverters
to couple to. If the genset is running as it seems it will be here, the
battery based inverters with transfer and charge the batteries and in most
cases fully charge them before the PV had much chance to do so because the
genset is likely producing double the charge rate of the PV. It can be
sickening to see the PV at Float by noon and the gensets running all
morning!
The o-t-g world is in serious need of large battery based inverters THAT
ARE EFFICIENT to tackle these challenges. As far as I know only Outback
fills the bill with the key word "efficient". Outback is limited to 10
inverters in a single (120/240 split) phase for 36kW and 9 in 3 phase 208VAC
for 32.4kW. The only way to make it work is as others have suggested - break
up the loads and distribution, maybe point-of-use smaller systems. In
addition, you should not connect more than 10 Outbacks to a single battery
bank.
Good industrial batteries are cheaper than diesel and pollute less while
increasing the life of the gensets and holding them at optimum loading.
I'm 4 years into a 17,000 s.f. o-t-g "home" in Mexico, I'm using 28
Outback inverters on 3 battery banks and 3 seperate distribution lines and 3
66kW Whisperwatt gensets. The EE designed the original 400M distribution
system w/transformers and 3 phase 480VAC like a good EE would, but when I
demonstrated the economics of spending a small fortune on copper to save a
massive fortune on solar he jumped on a transformerless distribution system!
The project has tripled it's load since my original design a few years ago.
I've spent 90% of these 4 years controlling loads, I've specified 98% of all
appliances, motors and misc. loads and have given my blessings to the rest.
I don't think we can make this palace any more efficient.
I'm echoing the others here and the Wreches Mantra - put most of your
efforts into efficiency and controlling loads, THEN look at solar and other
RE's.
Good luck and keep us posted....
-jeff o
[Non-text portions of this message have been removed]
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com