Thanks Allan,
John's Code Corner #66 addresses this issue. I have sent a copy to the AHJ,
but he states that he cannot "rely" on the article. At least he has it so
he can get up to speed if he wants to.
I had to send him a copy of the spec sheet that shows that the wire is
listed to UL 854. UL 854 is the spec for Service Entrance conductors where
it is specified that the wire is not marked "sunlight resistant" but has
been tested for the same.
Mark Frye
Berkeley Solar Electric Systems
2504 Webster St
Berkeley CA 94705-2504
(510) 685-3042
markf at berkeleysolar.com
www.berkeleysolar.com
-----Original Message-----
From: Allan Sindelar [mailto:allan at positiveenergysolar.com]
Sent: Friday, January 19, 2007 6:51 AM
To: RE-wrenches at topica.com
Subject: Re: GT series inverter certification [RE-wrenches]
Mark,
This is from my memory of a recent John Wiles PV/Code seminar, so I may be
incorrect here: USE-2 is sunlight-resistant whether marked or not.
You might contact John directly for assistance with this issue. 505
646-6105, or jwiles at nmsu.edu.
Allan at Positive Energy
----- Original Message -----
>Today I had a City
> of Berkeley inspector reject my installation because the USE-2 cable was
not
> marked "sunlight resistant".
>
> Mark Frye
> Berkeley Solar Electric Systems
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list