GT series inverter certification [RE-wrenches]
Joe Felker
joe.felker at alumni.stevens-tech.edu
Fri Jan 19 07:41:40 EST 2007
I have PDF versions of the manuals and they clearly state compliance in
the first section under safety. The text is below:
Regulatory ComplianceThe GT Inverter has complete on-board over-current,
over-temperature and anti-islanding protection, and meets U.S., Canadian
and international safety operating standards and code requirements:•UL
1741 1st Edition – Standard for Inverters, Converters, and Controllers
for Use in Independent Power Systems•CSA C22.2 No. 107.1-01 General Use
Power Supplies•IEEE C62.41 Recommended Practice on Surge Voltages in
Low-Voltage AC Power Circuits (Location Category B3).
Mark Frye wrote:
>
> Good Luck William,
>
> I do not know enough to be able to tell you that UL 1741 includes
> whatever
> IEEE requirements your AHJ is look for. There is no mention of IEEE
> standards in any of the Fronius ligature either.
>
> It must be the year of AHJ's going ape sh_t over solar. Today I had a
> City
> of Berkeley inspector reject my installation because the USE-2 cable was
> not
> marked "sunlight resistant".
>
> Please keep us informed about what you learn.
>
> Thanks,
>
> Mark Frye
> Berkeley Solar Electric Systems
> 2504 Webster St
> Berkeley CA 94705-2504
> (510) 685-3042
> markf at berkeleysolar.com
> www.berkeleysolar.com
>
>
> -----Original Message-----
> From: William Miller [mailto:wrmiller at charter.net]
> Sent: Thursday, January 18, 2007 5:17 PM
> To: RE-wrenches at topica.com
> Subject: GT series inverter certification [RE-wrenches]
>
>
>
> Friends:
>
> We have installed a bunch of GT series inverters. I have a job pending
> that specifies one but I can't get the AHJ to issue the permit because
> nowhere in the Xantrex literature is a specific indication that the unit
> is
> IEEE certified for grid connection and ground fault protection and UL
> tested for same. I've looked over the entire web site and all I see is
> a
> vague passing reference to it in the specifications page in the manual.
>
> We've e-mailed and called Xantrex to no avail (much to our
> disappointment). Does anyone know here this is published?
>
> William Miller
>
>
> __________________________________________________________________
> William Miller
> Miller Power and Communications
> Voice :805-438-5600 Fax: 805-438-4607
> email: wrmiller at mpandc.com
> http://mpandc.com
> License No. C-10-773985
> _____________________________________________________________
> Check out our latest project at
> http://mpandc.com/case_studies/pv_school/pv_school.html
>
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
>
>
>
Joe Felker
Engineering Manager
NABCEP Certified Solar PV Installer
The Solar Center
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list