William,
Don't see your drawing, but unless you are using shunt regulation,
those strings are protected from battery current feedback two ways.
1) by the controller itself and 2) by the battery/controller OC
device, these days most often a DC rated CB.
Granted that CB will be likely be too oversized to protect the PV
interconnect wires in a partial fault, but that event plus a shorted
controller is extremely unlikely. In a full-on short AND in the very
unlikely event the controller is somehow shorted as well, it should
break the circuit. There are no absolutes in electricity. Anything
"could" happen. We protect against the likely probabilities.
Bob-O
On Nov 20, 2006, at 6:11 PM, William Miller wrote:
>
>
>
>
>
> Friends:
>
> We have all learned that in grid-tie systems, string quantities of
> two or less do not require series fusing (and in some cases, string
> quantities of 3).
>
> I am wondering if that holds true for battery based systems.
> Specifically, if I have two series strings of modules, can I
> connect them together without fuses?
>
> How about if I have multiple pairs of strings? Can two series
> string groups be connected with fuses only between the groups of
> two strings?
>
> I have drawn a block diagram and, in this scenario, the two strings
> hard wired together are all protected from external fault current
> by the properly sized string fuse.
>
>
> Comments?
>
> William Miller
>
>
>
>
> __________________________________________________________________
> William Miller
> Miller Power and Communications
> Voice :805-438-5600 Fax: 805-438-4607
> email: wrmiller at mpandc.com
> http://mpandc.com
> License No. C-10-773985
> _____________________
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list