Hi William,
In a word, no.
Because it is possible for the controller to fail and back feed from
the battereis,
you could get big amps going the wrong way.
So you must fuse each series string, but if the series fuse rating is
high enough you might be able to get away
with having 2 in series.
jay
peltz power
On Nov 20, 2006, at 6:11 PM, William Miller wrote:
>
>
>
>
>
> Friends:
>
> We have all learned that in grid-tie systems, string quantities of
> two or less do not require series fusing (and in some cases, string
> quantities of 3).
>
> I am wondering if that holds true for battery based systems.
> Specifically, if I have two series strings of modules, can I
> connect them together without fuses?
>
> How about if I have multiple pairs of strings? Can two series
> string groups be connected with fuses only between the groups of
> two strings?
>
> I have drawn a block diagram and, in this scenario, the two strings
> hard wired together are all protected from external fault current
> by the properly sized string fuse.
>
>
> Comments?
>
> William Miller
>
>
>
>
> __________________________________________________________________
> William Miller
> Miller Power and Communications
> Voice :805-438-5600 Fax: 805-438-4607
> email: wrmiller at mpandc.com
> http://mpandc.com
> License No. C-10-773985
> _____________________________________________________________
> Check out our latest project at http://mpandc.com/case_studies/
> pv_school/pv_school.html
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://lists.topica.com/lists/RE-
> wrenches/read
>
> List rules & how to change your email address: www.mrsharkey.com/
> wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list