Hi Brad,
This is an excellent idea and should be pursued for future code
revisions for 690. Feeding the bus on the opposite end on commercial
panels is also quite easily achieved as many have a flexible bus
design. On residential systems John W. has argued that the homeowner
or unknowing electrician could move a breaker mounted at the bottom
of a panel - but bottom fed lugs would eliminate this problem. Very
elegant solution.
Anyone out there willing to champion this idea to the powers that be?
When's the next code revision input period opening up?
Thanks Brad!
Jeff C.
>The other possibility around the bus size issue is to get the code
>rewritten to allow a larger grid intertie at the opposite end of the
>busbar from the feedin main breaker. I believe this makes it impossible
>to overload the bus in most residential panels. This would help in not
>having to oversize AC panels for combining multiple inverter outputs
>also. Or maybe one of the big panel mfg could put in lugs at both ends
>of the bus for feedin and get UL on it for that purpose.
>
>Brad
>
>
>Allan Sindelar wrote:
>>
>> If the two functions could somehow be separated, the range of
>> applications would be increased, as it's only the sell function that is
>> subject to the 120% bussbar limitation of 690-64(b)(2).
>>
>>
>
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
>
>List rules & how to change your email address:
>www.mrsharkey.com/wrenches/etiquette.php
>
>Check out participant bios: www.mrsharkey.com/wrenches/
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
--
~~~~~~~~~~~~~
Jeff Clearwater
Village Power Design
Sustainable Energy & Water Solutions for Home & Village
http://www.villagepower.com
gosolar at villagepower.com
NABCEP (tm) Certified Solar PV Installer
530-470-9166
877-SOLARVillage
877-765-2784
65 Schoolhouse Rd
Amherst, MA 01002
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~`~
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list