Backfeeding a 200 amp panel with an Outback 3648 [RE-wrenches]
bbassett at rockisland.com
bbassett at rockisland.com
Wed Oct 18 20:13:42 EDT 2006
I have also thought that a grid feed circuit separate from the bypass
feed would be a good feature on the Outback inverters, but for an
additional reason. Here in WA state we have production based incentives
that have recently been put into action (finally). The largest utility,
PSE, is charging the customer for the production meters that they are
putting in these systems. This amounts to $160 for a simple grid tie,
and up to $955 for a 120/240 battery based grid tie system (using
Outback's system of using form 12S meters, two for 120/240).
Unfortunately, the law was not written to prohibit this for the
incentive metering (but fortunately was for net metering on the main
utility meter). The Sunny Island gets around this problem nicely, but it
would be an advantage to use a WA made inverter since the incentive
rises from $0.15kWh to $0.18kWh if it is. With separate grid tie and
bypass circuits this would then use the easy, less expensive metering.
The other possibility around the bus size issue is to get the code
rewritten to allow a larger grid intertie at the opposite end of the
busbar from the feedin main breaker. I believe this makes it impossible
to overload the bus in most residential panels. This would help in not
having to oversize AC panels for combining multiple inverter outputs
also. Or maybe one of the big panel mfg could put in lugs at both ends
of the bus for feedin and get UL on it for that purpose.
Brad
Allan Sindelar wrote:
>
> If the two functions could somehow be separated, the range of
> applications would be increased, as it's only the sell function that is
> subject to the 120% bussbar limitation of 690-64(b)(2).
>
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list