Thanks William,

I think we see eye to eye on this. I too believe that the intent of the 
article is to require OCP on the PV system circuit prior to 
“connection” with the premise wiring. Also no other loads or 
sources of supply are allowed on the PV system side of that OCP.

When a circuit breaker, slotted into a buss is available, the point of 
connection is the terminals of the circuit breaker.  When there is no 
circuit breaker available a fused disconnect must be used. By it’s 
very nature the fused disconnect must be tapped into an available feeder 
somewhere along the premise wiring.  Without a tap there is no 
functioning fused disconnect.  The code allows the use of the 
disconnect, therefore it must allow the tap. The point of connection of 
the PV system is now the terminals on PV system side of the fused 
disconnect.

MPF

William Miller wrote:
> 
> Mark:
> 
> I have no history with the writing of this section, but in my humble 
> opinion, the obvious reason for (B) (1) is so the feeders from the 
> inverter 
> have over-current protection and a way to turn off AC from the grid to 
> that 
> feeder.
> 
> As per your Question 2:  I did not write the section, but in reading it 
> I 
> see that it REQUIRES, not prevents  a dedicated disconnect.
> 
> Are you tapping the feeder to an existing disconnect that feeds another 
> load?  If so, if it is otherwise legal and you provide another 
> disconnect 
> dedicated to the grid-tie system, you are correct.
> 
> William Miller
> 
> 
> At 08:20 AM 9/15/2006, you wrote:
> 
> >Can any veteran wrench address the issue of the history and intent of
> >the code relative to Article 690.64 (B) (1)?
> >
> >Was there a particular reasoning such that it's intent was to prohibit
> >making a feeder tap to a fused disconnect?
> >
> >If so can anyone describe a way that a fused disconnect can be utilized
> >in anyway to make the connection of a PV system circuit to the premise
> >wiring.
> >
> >Mark Frye
> >Berkeley Solar Electric Systems


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------




More information about the RE-Wrenches mailing list