Point of Connection Intent [RE-wrenches]

William Miller wrmiller at charter.net
Fri Sep 15 12:04:36 EDT 2006


<x-flowed>

Mark:

I have no history with the writing of this section, but in my humble 
opinion, the obvious reason for (B) (1) is so the feeders from the inverter 
have over-current protection and a way to turn off AC from the grid to that 
feeder.

As per your Question 2:  I did not write the section, but in reading it I 
see that it REQUIRES, not prevents  a dedicated disconnect.

Are you tapping the feeder to an existing disconnect that feeds another 
load?  If so, if it is otherwise legal and you provide another disconnect 
dedicated to the grid-tie system, you are correct.

William Miller


At 08:20 AM 9/15/2006, you wrote:

>Can any veteran wrench address the issue of the history and intent of
>the code relative to Article 690.64 (B) (1)?
>
>Was there a particular reasoning such that it's intent was to prohibit
>making a feeder tap to a fused disconnect?
>
>If so can anyone describe a way that a fused disconnect can be utilized
>in anyway to make the connection of a PV system circuit to the premise
>wiring.
>
>Mark Frye
>Berkeley Solar Electric Systems


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------



</x-flowed>


More information about the RE-Wrenches mailing list