Single vs Distributed Inverters? [RE-wrenches]

Max Balchowsky max at seesolar.com
Fri Jun 9 22:51:19 EDT 2006


We've done both - 60 and 70 KW systems using one inverter (satcon) and 120
KW plus using sunny centrals. 30 to 50 Kw systems using SMA and PV powered
multiple smaller inverters. One nice feature with SATCON is that it comes
ready to use with online monitoring........ It depends on the location and
type of facility for us.

Max Balchowsky
SEE Systems


-----Original Message-----
From: Jeffery Wolfe, Global Resource Options
[mailto:jeff at globalresourceoptions.com] 
Sent: Friday, June 09, 2006 7:07 PM
To: RE-wrenches at topica.com
Subject: RE: Single vs Distributed Inverters? [RE-wrenches]


David,

It's your first large system. You know string inverters. The engineering
on a large system can be very similar to a small system if you use the
string inverters. Less to learn on a commercial job that way. And
probably less expensive, depending upon exact stringing.

Go with a large inverter, then you get to learn a new product line for
engineering, special order some equipment, wait for it, learn how to
install, commission, and possibly troubleshoot it.

I'd stick with the string inverters unless you're planning on doing a
lot of these, and then you could try to optimize. But we've found that
the string inverters are less expensive, installed (if you've got
space), than any larger inverter, up to 50 or 60 kW of capacity.

Depending upon module, you can probably use 6 SMA 6000's, with about 7
kW on each. It is even balanced on the phases!

Jeff
Jeff Wolfe
Global Resource Options, Inc., Solar Energy Solutions

Original Message:
-----------------
From: David Blecker blecker at seventhgenergy.org
Subject: Single vs Distributed Inverters? [RE-wrenches]

Wrenches,

We're trying to design our first large PV system - 40kW grid-tied,
roof-mount, 208V grid - and we're wrestling with the inverter selection.
I've seen traffic on this list with seemingly split opinions as to go
with a single large inverter or to use multiple parallel smaller
inverters.  So, anyone care to re-open that thread and share your
opinions and experiences?

Thanks in advance.  Hope to see all you at the Energy Fair!
www.the-mrea.org

-David



----------
David Blecker, PE
Seventh Generation Energy Systems, Inc.
Ph:  608-467-1518
Cell: 608-335-3375
Fax: 866-762-7496 (toll-free)
Web: www.seventhGenergy.org


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------





More information about the RE-Wrenches mailing list