Single vs Distributed Inverters? [RE-wrenches]
Jeffery Wolfe, Global Resource Options
jeff at globalresourceoptions.com
Fri Jun 9 22:06:57 EDT 2006
David,
It's your first large system. You know string inverters. The engineering
on a large system can be very similar to a small system if you use the
string inverters. Less to learn on a commercial job that way. And
probably less expensive, depending upon exact stringing.
Go with a large inverter, then you get to learn a new product line for
engineering, special order some equipment, wait for it, learn how to
install, commission, and possibly troubleshoot it.
I'd stick with the string inverters unless you're planning on doing a
lot of these, and then you could try to optimize. But we've found that
the string inverters are less expensive, installed (if you've got
space), than any larger inverter, up to 50 or 60 kW of capacity.
Depending upon module, you can probably use 6 SMA 6000's, with about 7
kW on each. It is even balanced on the phases!
Jeff
Jeff Wolfe
Global Resource Options, Inc., Solar Energy Solutions
Original Message:
-----------------
From: David Blecker blecker at seventhgenergy.org
Subject: Single vs Distributed Inverters? [RE-wrenches]
Wrenches,
We're trying to design our first large PV system - 40kW grid-tied,
roof-mount, 208V grid - and we're wrestling with the inverter selection.
I've seen traffic on this list with seemingly split opinions as to go
with a single large inverter or to use multiple parallel smaller
inverters. So, anyone care to re-open that thread and share your
opinions and experiences?
Thanks in advance. Hope to see all you at the Energy Fair!
www.the-mrea.org
-David
----------
David Blecker, PE
Seventh Generation Energy Systems, Inc.
Ph: 608-467-1518
Cell: 608-335-3375
Fax: 866-762-7496 (toll-free)
Web: www.seventhGenergy.org
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list