Eric & All:
I am STRONGLY in consensus with Marco's Post. There are cheaper
alternatives out there, Crouse-Hinds is one example, but I don't find
the extra cost (like <.01% of the job) is worth it. Square D HU's come
with Arc Shields. There are no exposed energized terminals on the line
side. I don't like or feel comfortable with using Disco's without this
feature, but have had to for "Program Budget" purposes in the past.
Square D's economy version is at the following link (Without Arc
Shields. Not the same quality as the HU):
http://ecatalog.squared.com/catalog/html/sections/03/17203002.htm#999461
Note: The current HU link is:
http://ecatalog.squared.com/catalog/html/sections/03/17203006.htm
Grounding kits are at the following link: (Same catalog...Just click
Next at bottom of page)
http://ecatalog.squared.com/catalog/html/sections/03/17203010.htm
Good Luck, Eh!
Matt Lafferty
Universal Energies Institute
mlafferty at universalenergies.com
(916) 422-9772
(916) 628-7694 Cell
(916) 914-2247 Fax
www.universalenergies.com
-----Original Message-----
From: Marco [mailto:marco at pvthawaii.com]
Sent: Wednesday, August 06, 2003 4:52 PM
To: RE-wrenches at topica.com
Subject: RE: utility disconnect for grid-tie [RE-wrenches]
Eric,
I'm sold on the Square D "H" series heavy-duty 3-pole disconnects that
are rated for 600V AC and DC. You can get them both for indoor and
outdoor NEMA3R applications.
For example:
HU ("U" meand unfused) 361 is rated for 30A
HU 362 60A
HU 363 100A
HU 364 200A
HU 365 400A
The HU 361RB is for outdoor applications.
Here's a link to the Sq.D disconnects website:
http://www.squared.com/us/products/safetysw.nsf/DocumentsByCategory/43D6
81D7
C3197658852568460060B1B5
good luck!
marco
proVision technologies
Hilo, Hawai'i
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list