utility disconnect for grid-tie [RE-wrenches]

Marco marco at pvthawaii.com
Wed Aug 6 19:51:33 EDT 2003


Eric,

I'm sold on the Square D "H" series heavy-duty 3-pole disconnects that are
rated for 600V AC and DC.  You can get them both for indoor and outdoor
NEMA3R applications.

For example:
HU ("U" meand unfused) 361 is rated for 30A
HU 362 60A
HU 363 100A
HU 364 200A
HU 365 400A

The HU 361RB is for outdoor applications.

Here's a link to the Sq.D disconnects website:
http://www.squared.com/us/products/safetysw.nsf/DocumentsByCategory/43D681D7
C3197658852568460060B1B5

good luck!
marco
proVision technologies
Hilo, Hawai'i

-----Original Message-----
From: Eric Smiley [mailto:Eric_Smiley at bcit.ca]
Sent: Wednesday, August 06, 2003 12:52 PM
To: RE-wrenches at topica.com
Subject: utility disconnect for grid-tie [RE-wrenches]



I'm trying to specify a disconnect switch for grid-tie PV that will meet
our utilities requirements at the least cost. This requirement for an
essentially redundant switch has been used by many utilities and I would
appreciate finding out what others are using.

The switch must be outdoor rated, but in addition our utility requires
the switch to:

(a) Be capable of being energized from both sides; and
(b) Plainly indicate whether in the "open" or "closed" position; and
(c) Have contact operation verifiable by direct visible means; and
(d) Have provision for being locked in the "open" position; and
(e) Conform to Sections 14, 28, and 36 of [the Canadian Electrical Code]
if it includes an
overcurrent device; and
(f) Be capable of being opened at rated load; and
(g) Be capable of being closed with safety to the operator with a fault
on
the system; and
(h) Disconnect all ungrounded conductors of the circuit simultaneously;
and
(i) Bear a warning to the effect that inside parts can be energized when
the
disconnecting means is open; and
(j) Be readily accessible.

Regarding item (c) our utility is allowing, "A low-voltage safety
switch, where the cover can be opened when the switch is in the "open"
position thus providing visual verification that the contacts are
open,..."
Which means we don't need a switch with a window in it (phew)- an even
more expensive option.

Eric Smiley

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------






More information about the RE-Wrenches mailing list