Brad,

I'm not sure that this question got answered. John Berdner probably knows
better than I, but my understanding is that 13A is a continuous rating. The
issue with a disconnect is what happens when it opens anyway, so it is a bit
different than wire. However--the proper way to size is based on 690.8 which
says you take the total Isc of parallel strings and multiply by 1.25. The
Isc of the 165-Watt module is 4.77 amps so max current is 12 amps (4.77A x 2
x 1.25 = 11.925).

Some bright guy must have picked that 13 amp number.

Bill.


-----Original Message-----
From: Brad Bassett [mailto:bsbassett at earthlink.net]
Sent: Wednesday, February 12, 2003 9:18 AM
To: RE-wrenches at topica.com
Subject: SPAM: RE: 600 VDC switches [RE-wrenches]


John,

I have not seen an answer to this question. If you feed an SB with two
strings of modules, the 13A limit is likely to be exceeded if it is not
rated for continuous. With the 165's it's exceeded even at PV 125%.

Thanks,
Brad


William Miller wrote:
> The rating is for 13 amps per pole.  Is this de rated for continuous, or
> for PV?
>
> Thanks again,
>
> William
>
>




Brad Bassett
Schott Applied Power
Tumwater, WA office
bsbassett at earthlink.net

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael_welch at sbcglobal.net

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
==^================================================================






More information about the RE-Wrenches mailing list