600 VDC switches [RE-wrenches]
Bill Brooks
billb at endecon.com
Thu Feb 13 18:41:10 EST 2003
Brad,
Tim Townsend, a colleague of mine talked directly with Square D and gives
this information:
"I spoke with Bob Miller and Tom Keene of Square D about this -- they said
the 13 A [PER POLE] test was done at 250 Vdc and 6000 operations
(successfully), and also at 18 A [PER POLE] at 600 Vdc and 50 operations
(also successfully)." Tim
The 250 Vdc number is for the differential between Vmp and Voc under load
(600V-350V=250V). The 600Vdc test is for worst case positive pole to ground
short circuit. John B. can correct me if I have the information messed up.
Hope this helps.
Bill.
-----Original Message-----
From: Brad Bassett [mailto:bsbassett at earthlink.net]
Sent: Wednesday, February 12, 2003 9:18 AM
To: RE-wrenches at topica.com
Subject: SPAM: RE: 600 VDC switches [RE-wrenches]
John,
I have not seen an answer to this question. If you feed an SB with two
strings of modules, the 13A limit is likely to be exceeded if it is not
rated for continuous. With the 165's it's exceeded even at PV 125%.
Thanks,
Brad
William Miller wrote:
> The rating is for 13 amps per pole. Is this de rated for continuous, or
> for PV?
>
> Thanks again,
>
> William
>
>
Brad Bassett
Schott Applied Power
Tumwater, WA office
bsbassett at earthlink.net
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
==^================================================================
More information about the RE-Wrenches
mailing list