Christopher's advice way back then. 9) L-16's in series for a 54 Vdc nominal
and sell at 60 Vdc through 4) SW5548's. It has worked well...
-jeff
> From the Solar, Wind & Hydro Powered office of:
> Jeff Oldham
> Gaiam- Real Goods & Jade Mountain
> Design & Consulting Group
> 11755 Mid. Mtn. Rd.
> Potter Valley, CA 95469 USA
>
> Ph: 303.222.3814
> Fax: 707.743.1820
>
> www.solardevelopment.com
>
> "When you turn to face the Sun all shadows fall behind you"
> - Old African Proverb
>
-----Original Message-----
From: Travis Creswell, Ozark Solar [mailto:ozsolar at ipa.net]
Sent: Wednesday, May 29, 2002 12:21 PM
To: RE-wrenches at topica.com
Subject: Re: On grid w/battery and MPPT [RE-wrenches]
Christopher and others,
I had this idea several years ago and wondered what you thought about it.
Assuming one was to use a grid tie battery based inverter and 6 volt
batteries. Instead of the standard battery bank that floated @ 53.6 volts,
use a battery bank that floated @ 59.6 by adding one more 6 volt battery.
This also assumes that you can appropriately adjust the parameters of the
float and bulk voltages. Would this system produce more kWh's annually
since you were running the array closer it's maximum power point? I see
that I can adjust the Float and Bulk voltages on my SW4048 up to 64.0.
Travis Creswell
Ozark Energy Services
----------
>From: Christopher Freitas - OutBack Power <cfreitas at outbackpower.com>
>To: RE-wrenches at topica.com
>Subject: RE: On grid w/battery and MPPT [RE-wrenches]
>Date: Wed, May 29, 2002, 11:51 AM
>
>Even in the alternate universe called California the performance of a
>system without MPPT will be different if the batteries are located in a
>conditioned space versus an exposed location as in Bill Brooks example.
>
>
>Another factor affecting the performance will be the nominal system
>voltage - a 48 vdc system will benefit more from a MPPT than a 24 vdc
>system for several reasons, which we can discuss more if people are
>interested...
>
>I am very interested in seeing performance comparisons testing of
>products by a third party - as long as the raw data is made available
>for review and a way to publicly comment on the results is provided
>(hint-hint).
>
>Christopher Freitas
>OutBack Power Systems, Inc.
>cfreitas at outbackpower.com www.outbackpower.com
>Tel 360 435 6030 Arlington WA USA
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-Wrenches
mailing list