On grid w/ 54vdc battery [RE-wrenches]

Christopher Freitas - OutBack Power cfreitas at outbackpower.com
Wed May 29 17:20:07 EDT 2002


Yes - I also did a number of systems with 54 vdc batteries - it will 
improve the performance for systems in cool climates (such as Colorado 
or the Sierra Nevada mountains.  

The main problem was the lack of memory for the setpoints required.  I 
did do one system where I adjusted the resistance of the temp comp 
sensor to make it think the batteries where cold, raising the settings - 
which worked better than adjusting the settings.  Still not perfect 
however.  

The difficult part is setting the charge controllers to prevent them 
from allowing the voltage to get to high and cause the inverter to shut 
down and to not trip into float, reducing the PV array's output power. 
The bottom line is that the PV controllers (MPPT or not) needs to "talk" 
with the inverters to prevent conflicts from occurring (which is what we 
at OutBack are doing with our new products).

Christopher Freitas
OutBack Power Systems, Inc.
cfreitas at outbackpower.com  www.outbackpower.com
Tel 360 435 6030  Arlington WA USA

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================




More information about the RE-Wrenches mailing list