Trace Charge Controller Ratings [RE-wrenches]

Ray Walters remotech at taosnm.com
Sun Apr 28 20:47:14 EDT 2002


I use class T pullout disconnects from Boltswitch. UL listed, we make our
own enclosures. I know all of you UL freaks are cringing, but I cringe at
breaker only systems or the overpriced breaker + fuse option.
Why did everyone quit using the Boltswitch disconnect anyway?

Ray


>   "I am still wondering how Trace gets away with using only the
>   Heinemann breakers as primary protection. While the breakers are rated at
>   25,000 AIC for DC circuits, who wants their equipment to handle that
>   current for the delay time required to trip this breaker"
>
>I agree.  we always install a class T fuse right next to the positive
>terminal of the battery bank with about 8" long #4/0 cable.  Then we run to
>the Heinermann breakers in the Trace panel.  This also gives the added
>protection in case the battery box and inverter are located in different
>rooms separated by a wall, with much higher potential for cutting or a short
>between the battery box and the inverter dis-connect that could start a
>fire.

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================




More information about the RE-Wrenches mailing list