Trace Charge Controller Ratings [RE-wrenches]

Allan Sindelar allan at positiveenergysolar.com
Wed Apr 24 16:12:03 EDT 2002


Wrenches,
I forwarded Eric's question about 100% rating on Trace DC disconnects to
John Wiles. Below is his response.
Allan @+NRG

----- Original Message -----
From: "John Wiles" <jwiles at nmsu.edu>
To: "Allan Sindelar" <allan at positiveenergysolar.com>; "Pagan MacKay"
<Pagan.MacKay at traceengineering.com>
Sent: Wednesday, April 24, 2002 1:47 PM
Subject: Re: Fw: Re:Trace Charge Controller Ratings [RE-wrenches]


> Dear Allan:
>
> The basic Heinemann 250 amp and 175 amp breakers are listed for
> operation at 100% duty.  According to NEC requirements, to be able to
> use that rating, Trace would have to have had the breakers tested and
> evaluated in the DC 250 enclosure at 100%.  The testing would have to
> include single breakers and double breakers.  Their listing
> information will tell the story and if so, a label should probably be
> added to the inside of the DC 250 enclosures.  It might even allow
> them to justify the use of 4/0 AWG cables on the SW4024, but that is
> another story.
>

> >----- Original Message -----
> >From: "Eric Smiley" <Eric_Smiley at bcit.ca>
> >>  Is the DC 175/DC 250 Disconnect from Xantrex rated 100%? There is no
> >>  indication on the enclosure (or in the instructions)  that it is rated
> >>  100% and that is what the inspector wants to see.
> >>

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================




More information about the RE-Wrenches mailing list