on 4/22/02 9:34 AM, Kirk Herander at kirk at vtsolar.com wrote:

> In regard to the furnace thread, I recently had to remove the phantom load
> effect of a multiple-zone hydronic boiler. Each zone has a dedicated Taco
> circulator instead of a zone valve. The pumps are energized through a Taco
> control box, based on the 24vac t-stat closure for each respective zone. We
> used double pole, single throw line voltage thermostats. The main boiler /
> control 120vac power is paralleled through pole 1 of each thermostat. Pole 2
> of each t-stat is wired into the Taco control box. Whenever there a T-stat
> calls for heat, the boiler and controls are powered up by 120 vac, and the
> the 24 vac closure is made, instructing the individual circulator to turn
> on.
> t-stat part# is Mcmaster-Carr 17395K95
> 
> Vermont Solar Engineering - a Xantrex / Trace Certified Dealer
> Kirk Herander
> PO Box 697
> Burlington, VT. 05402
> www.vermontsolar.com
> www.backeastsolar.com
> 800.286.1252 - 802.863.1202
> fax 802.863.7908
> 
> - - - -
> To send a message: RE-wrenches at topica.com
> 
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
> 
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
> 
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
> 
> Hosted by Home Power magazine
> 
> Moderator: michael.welch at homepower.com
> 
> 
> 
  How did you get the boiler auto vent damper to close when the AC is
abruptly shut off? The boilers I've used all need a continued supply of
120VAC for about 15 seconds after the thermostat is satisfied to allow time
for the damper to close, thus saving heat. A relay timer can solve this
problem.

Tom Simko
Skyline Solar
Idaho 
  

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================




More information about the RE-Wrenches mailing list